#26315 - 06/05/03 11:58 PM connecting two ATS to one generator.  
PETERANTHONY  Offline
Junior Member
Joined: Jan 2003
Posts: 2
MERRILLVILLE,IN,46410
I need some technical help I have a job to connect two transfer switches and one generator tha means any power failer on the normal feed to any of ATS shuold start the genrator . have never don that befor.
thanks for any help


Work Gear for Electricians and the Trades

#26316 - 06/06/03 06:49 AM Re: connecting two ATS to one generator.  
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
peteranthony,
the start signal to about all gensets is a simple dry closure, so a start signal from either should be fine, that said, why do you need a signal from both?

Is there a possibility that if the power is out on #1, it would still be on for #2? A signal from either one should be sufficient.


#26317 - 06/06/03 09:26 AM Re: connecting two ATS to one generator.  
Trainwire  Offline
Member
Joined: Mar 2002
Posts: 360
Strasburg,PA,USA
The only thing I see that would need to be incorporated, is some sort of a run switch, where by if one xfer switch starts it, the other start circuit is locked out, Xfer is still enabled, but the start sequence is interupted. Depending on the internal engineering of the xfer switch, that may already be accomplished.

You might want to look at total start load to make sure that if both tried to come online at the same time, you wouldn't overload the generator, a timer circuit on one would sove that. It means that if it(the one with the timer) came on first, the timer would have to time out before it would xfer, a few seconds at most.

It's not hard to glum out. Just takes a little thinking.

TW


#26318 - 06/07/03 12:22 AM Re: connecting two ATS to one generator.  
PETERANTHONY  Offline
Junior Member
Joined: Jan 2003
Posts: 2
MERRILLVILLE,IN,46410
the generator is abble to handel the load but we need to be able to start from any ats.
that is when there is a problem in any of the three defrent load by the way this is fora medical building any idia is aprciated.



Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7596 MB (Peak: 0.8909 MB) Zlib enabled. Server Time: 2017-04-26 09:56:06 UTC