connecting two ATS to one generator. #26315
06/05/03 10:58 PM
06/05/03 10:58 PM
P
PETERANTHONY  Offline OP
Junior Member
Joined: Jan 2003
Posts: 2
MERRILLVILLE,IN,46410
I need some technical help I have a job to connect two transfer switches and one generator tha means any power failer on the normal feed to any of ATS shuold start the genrator . have never don that befor.
thanks for any help

Work Gear for Electricians and the Trades
Re: connecting two ATS to one generator. #26316
06/06/03 05:49 AM
06/06/03 05:49 AM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
peteranthony,
the start signal to about all gensets is a simple dry closure, so a start signal from either should be fine, that said, why do you need a signal from both?

Is there a possibility that if the power is out on #1, it would still be on for #2? A signal from either one should be sufficient.

Re: connecting two ATS to one generator. #26317
06/06/03 08:26 AM
06/06/03 08:26 AM
T
Trainwire  Offline
Member
Joined: Mar 2002
Posts: 360
Strasburg,PA,USA
The only thing I see that would need to be incorporated, is some sort of a run switch, where by if one xfer switch starts it, the other start circuit is locked out, Xfer is still enabled, but the start sequence is interupted. Depending on the internal engineering of the xfer switch, that may already be accomplished.

You might want to look at total start load to make sure that if both tried to come online at the same time, you wouldn't overload the generator, a timer circuit on one would sove that. It means that if it(the one with the timer) came on first, the timer would have to time out before it would xfer, a few seconds at most.

It's not hard to glum out. Just takes a little thinking.

TW

Re: connecting two ATS to one generator. #26318
06/06/03 11:22 PM
06/06/03 11:22 PM
P
PETERANTHONY  Offline OP
Junior Member
Joined: Jan 2003
Posts: 2
MERRILLVILLE,IN,46410
the generator is abble to handel the load but we need to be able to start from any ats.
that is when there is a problem in any of the three defrent load by the way this is fora medical building any idia is aprciated.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,597 Are you busy
180,402 Re: Forum
170,868 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9579 MB (Peak: 1.0882 MB) Zlib enabled. Server Time: 2018-01-23 09:37:05 UTC