GFI adjustment on QED Switchboards #26194
06/01/03 09:07 AM
06/01/03 09:07 AM
G
golf junkie  Offline OP
Member
Joined: Apr 2001
Posts: 507
York, NE
My current job has a Square D 1600A QED switchboard for a main with a GC-200 ground fault interupter.

The other day the entire building tripped off line interupting all the trades while we got things reset. I found out that the GFI comes from the factory set to the minimum trip point and I didn't know enough to adjust it at the time of installation.

I will get the desired trip point from the engineer, but I was wondering if anyone can walk me though this adjustment. The Square D rep said that it would be calibrated in amps or as a percentage. Thats about all I know. Any insight would be helpful.

thanks,
GJ

Work Gear for Electricians and the Trades
Re: GFI adjustment on QED Switchboards #26195
06/01/03 11:24 AM
06/01/03 11:24 AM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA

Re: GFI adjustment on QED Switchboards #26196
06/02/03 12:25 PM
06/02/03 12:25 PM
G
golf junkie  Offline OP
Member
Joined: Apr 2001
Posts: 507
York, NE
thanks Nick

That's exactly what i needed.

GJ

Re: GFI adjustment on QED Switchboards #26197
06/04/03 12:18 PM
06/04/03 12:18 PM
G
golf junkie  Offline OP
Member
Joined: Apr 2001
Posts: 507
York, NE
FWIW
I spoke with the engineer today. Rule of thumb is to set the trip-point at 30% of the service size. So we set the trip to 480A, service size is 1600. The delay was set to 0.1 sec.

GJ

Re: GFI adjustment on QED Switchboards #26198
06/04/03 06:06 PM
06/04/03 06:06 PM
G
Gwz  Offline
Member
Joined: Apr 2002
Posts: 197
Not Sq D equipment, but a couple of years ago had 4000A Switch, Fused at 3400Amps, 480 3Ø 4W system on a building I was inspecting.

It seemed the Contractor and the and the Engineering testing Company were not very co-operative in the 230-95(c) department.

The sensor was a donut around the neutral bus.

The Service was 10 parallel sets of 500Kcmil with 5 sets landed on one side of the donut and and the other 5 sets on the same side of the donut as the bus connection into the next compartment. Quite an ordeal to have the donut moved between the 10 neutrals and the bus connection to the next compartment as indicated by the one-line diagram for that Service Equipment.

After the sensor was relocated, twice that I know of, a line to ground short on a 4AWG circuit some 300' away from the 45 Amp fused switch in the switchgear 'line-up' tripped the 4000A GFI .

[This message has been edited by Gwz (edited 06-04-2003).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,561 Are you busy
180,362 Re: Forum
170,840 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9661 MB (Peak: 1.0994 MB) Zlib enabled. Server Time: 2018-01-20 13:18:18 UTC