Single Wire Earth Return #26114
05/30/03 07:24 PM
05/30/03 07:24 PM
J
jdevlin  Offline OP
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
I have been reading about SWER and how is used developing countries and Australia outback and is a poor system.
Well I was checking out the transformer on the pole in my back yard and it sure looks like it is hooked up SWER. The poles have 4 wires. 3 off them are the lines to the houses and the 4th is the high voltage. The transformer has 5 wires. The 2 that look like the primary have the high volt on one terminal and a wire coming down the pole to a ground rod the other. The other 3 go to the homes with the center one also connected to the ground. I live in the middle of a city in Ontario. This sure sounds like SWER. Is it?

Work Gear for Electricians and the Trades
Re: Single Wire Earth Return #26115
05/30/03 08:44 PM
05/30/03 08:44 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The primary and secondary share the same grounded conductor. It is not a SWER.
Don


Don(resqcapt19)
Re: Single Wire Earth Return #26116
05/30/03 09:22 PM
05/30/03 09:22 PM
E
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
Have you found this thread ?


Al Hildenbrand
Re: Single Wire Earth Return #26117
05/31/03 07:11 AM
05/31/03 07:11 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
jdevlin,
You're unlikely to have SWER in the middle of Ontario.
SWER systems are really only used where it is un-economic to run more than two wires, and I'm talking way out in the sticks!. [Linked Image]

Re: Single Wire Earth Return #26118
06/01/03 09:12 AM
06/01/03 09:12 AM
J
jdevlin  Offline OP
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
I read that thread. That is what got me thinking about this.
The primary has only one wire referenced to the ground rod. How is that different SWER just because the secondary is tied to the ground rod also.

Re: Single Wire Earth Return #26119
06/01/03 10:50 AM
06/01/03 10:50 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
One grounded conductor carries both the primary and secondary current. The earth is not being used as a grounded conductor.
Don


Don(resqcapt19)
Re: Single Wire Earth Return #26120
06/02/03 08:34 PM
06/02/03 08:34 PM
J
jdevlin  Offline OP
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
Ok I understand that. I was thinking from the primary side. I only have one wire coming in. Doesn't that mean the earth is used as the return to the power plant. That is what I thought SWER was.

Re: Single Wire Earth Return #26121
06/02/03 09:24 PM
06/02/03 09:24 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The common grounded conductor is connected to a conductor that returns to the power plant. The earth is not being used as a return.
Don


Don(resqcapt19)
Re: Single Wire Earth Return #26122
06/02/03 10:44 PM
06/02/03 10:44 PM
E
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
jdevlin

Take a close look at the neutral conductor in the seperate secondary wires that run from pole to pole. When the hot secondary conductors are broken so as not to connect two transformers together, the neutral will be kept continuous.

At each transformer, the secondary neutral will be bonded to the ground wire running down the pole to the butt plate (or ground ball or ground rod) as well as to the transformer can itself. The low side of the primary will be bonded to the inside of the can.

If there's cable TV and/or telephone on these poles, the support messengers for them will also be bonded to the same ground wire.

In my mind, I see the PoCo primary neutral interconnections as being similar to the way the NEC has us hook equipment grounds together out on branch circuits. . .if they are present at a location, they are all connected together. Kinda forms a web.


Al Hildenbrand
Re: Single Wire Earth Return #26123
06/03/03 05:52 AM
06/03/03 05:52 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Don,
Would these be autotransformers?

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Popular Topics(Views)
243,606 Are you busy
180,422 Re: Forum
170,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.003s) Memory: 1.0219 MB (Peak: 1.1976 MB) Zlib enabled. Server Time: 2018-01-24 07:44:30 UTC