Suplemental grounding electrode #25539
05/12/03 06:11 PM
05/12/03 06:11 PM
E
Electricmanscott  Offline OP
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
I read the NEC to say that if you use an underground water pipe as your grounding electrode you must suplement it with an addtional electrode which must be less than 25 ohms (250.56). I have only been installing one rod for the suplemental and that has been fine with inspectors, till now. I ran into one that wants two since I can't verify less than 25 ohms. I beleive he is right and have no problem with it but another electrician I know says he is just busting my chops. He seems to think the inspector can not say it is or is not less than 25 ohms thefore no addtional rod is required. What's the real deal. Thanks, Scott

Work Gear for Electricians and the Trades
Re: Suplemental grounding electrode #25540
05/12/03 06:39 PM
05/12/03 06:39 PM
E
Electric Eagle  Offline
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
They've been making us use 2 rods for a while around here. It's not that expensive, so I don't see a reason to argue about it, just do it.

Re: Suplemental grounding electrode #25541
05/12/03 09:00 PM
05/12/03 09:00 PM
N
NorthernLights  Offline
Member
Joined: Mar 2003
Posts: 10
Massachusetts
One of the towns in my area asks for 2 ground rods. When I ask about it, he threatened to actually bring out test gear to prove me wrong. I put in the 2 rods......like someone said, it's not that expensive and not worth the argument. This is not one of those arguments worth pursuing.

Re: Suplemental grounding electrode #25542
05/12/03 09:12 PM
05/12/03 09:12 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
For what it's worth....
We have been enforcing the 2 rods or <25 ohms for a while. You get the occasionsl argument from an EC, but my usual response is

Ground rod testing equipment is about $2000.00. You probably need a day to familiarize yourself with the gear, and some time to perform the test.
A second rod, clamp, wire, is about $20.00

Make it a financial decision.

PS: NJ interpertation of "let the AHJ test it, and prove it's NG" does not fly. The proof of test results is upon the installer, be it the homeowner or the EC.

Nuff said
John


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 19
Potseal 13
Popular Topics(Views)
243,514 Are you busy
180,311 Re: Forum
170,804 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 14 (0.004s) Memory: 0.9582 MB (Peak: 1.0885 MB) Zlib enabled. Server Time: 2018-01-17 01:10:17 UTC