Arc damage to meter socket bussing. Repair or replace? #25533
05/12/03 03:40 PM
05/12/03 03:40 PM
A
azcont  Offline OP
Junior Member
Joined: May 2003
Posts: 6
phoenix, AZ, Maricopa
Hello all,

First time on this board. Really like it so far. Thanks to all for the great posts on the many threads.

Residential panel with very minor arc damage to bussing and discoloration on one meter socket. A bolt loosened up after a power outage or had been loosening up over 20 years panel was installed.

I am mainly a commercial contractor but the customer is a family friend. I really don't know what the right thing to do is. I could buff out the busses and re-bolt. Or try to find replacement parts which I think will be difficult. Or I will need to replace the whole panel.

Not the area I am strongest in. I am reluctant to take on the liability of repairing a 20 year old panel that two-four other electricians/homewners have already added to with pool, spa, Malibu lights, Lighting and a few other additions.

At the same time I want to give this customer the best possible advice. Too bad I could not get the utility company to bear the burden. But the bus turned out to be loose not just a loose jaw on the meter.

What do you think? One to walk away from/turn to a bigger outfit. Or go ahead and rig it?

Thanks, Robert

Work Gear for Electricians and the Trades
Re: Arc damage to meter socket bussing. Repair or replace? #25534
05/12/03 04:33 PM
05/12/03 04:33 PM
S
SvenNYC  Offline
Member
Joined: Aug 2002
Posts: 1,691
New York City
If you are reluctant to take the responsibility for repairing this panel, the most prudent albeit expensive way to go is to replace it.

Also, even if you re-bolt it, wouldn't you run the risk of it going bad again in the future? Metal fatigue and all that....

At leat with a new panel, you're covered by a warrantee and you know it's new and the job was done right the first time.

Just my opinion....good luck

Re: Arc damage to meter socket bussing. Repair or replace? #25535
05/12/03 04:57 PM
05/12/03 04:57 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,344
I've told many that i can bandaid things today with no guarantee....

Same as a soup can for a muffler repair

Re: Arc damage to meter socket bussing. Repair or replace? #25536
05/12/03 06:13 PM
05/12/03 06:13 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Replace the panel.

Re: Arc damage to meter socket bussing. Repair or replace? #25537
05/12/03 09:13 PM
05/12/03 09:13 PM
M
mamills  Offline
Member
Joined: Nov 2001
Posts: 745
Wharton, Texas, USA
Hi Robert:
With all the additions which have been made over the years, it occurs to me that the time is right for an upgrade. In the interest of safety, you certainly can't go wrong. Best wishes. I hope the job goes well. [Linked Image]

Mike (mamills)

By the way, Welcome to ECN!!

[This message has been edited by mamills (edited 05-12-2003).]

Re: Arc damage to meter socket bussing. Repair or replace? #25538
05/12/03 09:28 PM
05/12/03 09:28 PM
A
azcont  Offline OP
Junior Member
Joined: May 2003
Posts: 6
phoenix, AZ, Maricopa
This problem has been weighing on my mind on an off today as my customer battles with local utility and original panel manufacturer.

I really thought from the minute I saw the panel with the meter out[Replact the panel you idiot]to myself. I just really needed some feedback on my thoughts. I appreciate all your posts.

I noticed on what I could read off the flaking old paper panel lable that the panel was rated for 150 amps. Later on the lable it was rated for 150 amps continuous. Which did not make sense to me. The main was a 200amp. Original? Who knows.

Thanks for the reassurance to sell the panel upgrade/changeout.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 12
Popular Topics(Views)
243,606 Are you busy
180,418 Re: Forum
170,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.004s) Memory: 0.9754 MB (Peak: 1.1188 MB) Zlib enabled. Server Time: 2018-01-24 05:59:02 UTC