Bonding panels #25239
05/01/03 07:23 PM
05/01/03 07:23 PM
R
rowd  Offline OP
Member
Joined: Sep 2002
Posts: 31
Park Forest, Illinois, USA
Can someone give me a inspectors definition of "bonding". I have 3 main panels in a residential building. The inspector says he wants the panels bonded together.
I thought they were "bonded together" already as the Metal pipe for each panels feeder wire goes back to the meter sockets which are "bonded" together with pipe and locknuts.
I don't understand what he's looking for when he says "bonded together".

Work Gear for Electricians and the Trades
Re: Bonding panels #25240
05/01/03 07:58 PM
05/01/03 07:58 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Bonding bushing at the meter sockets?


Ron
Re: Bonding panels #25241
05/02/03 05:04 AM
05/02/03 05:04 AM
Z
zapped208  Offline
Member
Joined: Feb 2003
Posts: 197
Somewhere in USA
rowd,- More than likely he is wanting a bonding jumper between all 3 panelboards, 2002 NEC 250.66


Shoot first, apologize later.....maybe
Re: Bonding panels #25242
05/02/03 06:17 AM
05/02/03 06:17 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Did you install a separate EGC?
Generally, the conduit feeding the panels, if continuous and tight should be sufficient to serve as an EGC and a bonding means.
See 250.96
Are there any eccentric or concentric rings left at the conduit connection point? Although bonding bushings are only required for Services, per 250.92, and 250 Volts or more, per 250.97, he may have concerns about loose conduit connections.
Ask him for specific references!

[This message has been edited by Redsy (edited 05-02-2003).]

Re: Bonding panels #25243
05/04/03 08:48 PM
05/04/03 08:48 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Rowd,

I would call the AHJ and ask him. We would only be guessing as to what he really means. As an AHJ I don't mind when someone calls me up and asks, "What did you mean?" I would be more than happy to explain to him what I saw, and what needs to be done in order to get the job done. After all he might be right and I just didn't see something.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,263
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,516 Are you busy
180,314 Re: Forum
170,811 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9658 MB (Peak: 1.1050 MB) Zlib enabled. Server Time: 2018-01-17 07:05:50 UTC