Apt. Service question #24719
04/20/03 08:01 PM
04/20/03 08:01 PM
S
Shinkman  Offline OP
Junior Member
Joined: Nov 2002
Posts: 6
Pennsylvania
How do you guy's run your service cable for a duplex apartment? Each apt load will require 100a. Is the general procedure to run 200a service cable from taps into 200a service disconnects and then into two 100a meter sockets? How do different area's of the country do it?? Thanks

Work Gear for Electricians and the Trades
Re: Apt. Service question #24720
04/20/03 09:30 PM
04/20/03 09:30 PM
R
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
If this is an apartment building with a first and second floor, it's a single riser into a two gang meter fitting (pan), then from each meter to the separate panels.

Or are these dwellings side by side and just share a common wall between them, but have their own property lines. If this was the case I would expect a seperate rise on each side of the building and a single gang meter on each separately owned property.

Russ

Re: Apt. Service question #24721
04/20/03 09:51 PM
04/20/03 09:51 PM
Obsaleet  Offline
Member
Joined: Apr 2003
Posts: 362
Pa
Meter first then 2g meter base then disconnect. Some power co will allow meter bases with disconnects built in. Makes it real nice.

Ob


Choose your customers, don't let them choose you.
Re: Apt. Service question #24722
04/21/03 07:10 AM
04/21/03 07:10 AM
S
Shinkman  Offline OP
Junior Member
Joined: Nov 2002
Posts: 6
Pennsylvania
Russ, What type of meter socket do you bring the 200 amp service cable into? Do you use two 200amp sockets ganged together or two 100amp meter sockets ganged (or nippled) together? Out of meters to panel with 100a se cable for both.

Re: Apt. Service question #24723
04/21/03 08:06 AM
04/21/03 08:06 AM
W
wocolt  Offline
Member
Joined: Dec 2002
Posts: 110
Sinkman
The way we do it is to bring the 4/0 al cable into a double 100 amp meter base. the actual set-up has three (3) actual sections the middle section is a blank cover under which is the bus for the two meter sockets the incoming cable is landed in this middle section, there are three lugs to land to.
then from each meter section No.2 seu cable is run to either a disco or a service panel.

Wm.Colt

Re: Apt. Service question #24724
04/21/03 01:49 PM
04/21/03 01:49 PM
S
Shinkman  Offline OP
Junior Member
Joined: Nov 2002
Posts: 6
Pennsylvania
Wm, By double 100amp meter do you mean two 100amp meters ganged together or is it a special meter with more lugs inside?

Re: Apt. Service question #24725
04/21/03 06:09 PM
04/21/03 06:09 PM
Z
zapped208  Offline
Member
Joined: Feb 2003
Posts: 197
Somewhere in USA
Shinkman,- A 2 gang meter socket, base, or pan is one continuous assembly, as wocolt has explained, for 2 meters. Where in P.A. are you?, PP&L territory ?


Shoot first, apologize later.....maybe
Re: Apt. Service question #24726
04/21/03 06:29 PM
04/21/03 06:29 PM
W
wocolt  Offline
Member
Joined: Dec 2002
Posts: 110
sHinkman;
Sorry for the misspelling.
Yes it is a complete assembly especially for 2-single-dwelling units or apartments.
As I said the ones I like have actually three spaces but they do make them with only two where one end is a bit larger for the service conductors to enter.
They are also known as a '2-banger' or double gang meter base.
Siemens also makes them with the disconnects/Main breaker already installed.


Wm.Colt

Re: Apt. Service question #24727
04/30/03 07:18 PM
04/30/03 07:18 PM
W
Wirenuttt  Offline
Member
Joined: Nov 2002
Posts: 267
Massachusetts
Some areas require a house meter along with the meters per apt. If it's rented apt. with a common egress then the common hallways, basement, outside lights and smokes have to be on a house meter--- 3-gang meter bank, can get them with breakers and run to each unit with an MLO. Electricians have their prefernces on this. Hope this helps.
~Ange

Re: Apt. Service question #24728
05/01/03 06:08 AM
05/01/03 06:08 AM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Shinkman, 200 amp total (I think its actually 225) 100 amp per position.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004