ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
1913 American Electrician's Handbook
by annemarie1. 07/27/17 03:10 PM
600 KW 120/208 3 Phase Y protection
by Yooperup. 07/24/17 12:20 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
Housebilding DIY wiring
Popular Topics(Views)
239,371 Are you busy
174,826 Re: Forum
167,217 Need opinion
Who's Online Now
0 registered members (), 38 guests, and 5 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#2381 - 07/06/01 02:05 PM cable bury depth  
xformer  Offline
Junior Member
Joined: Jul 2001
Posts: 3
Lowell,MI,USA
Hi all, I am a first time poster to this forum. My question is about the burial depth of 12/2 w/GND cabling that I will be running out to my garden area for a duplex. Also, will conduit be needed where the cabling comes up out of the ground? Are these subject to local codes? If so, I am in GR Michigan.
Thanks in Advance,
Dave


Work Gear for Electricians and the Trades

#2382 - 07/06/01 03:55 PM Re: cable bury depth  
Anonymous
Unregistered

>My question is about the burial depth of 12-2 w/GND cable
Sounds like it will be UF cable hauling 120 V.
18" inches should work.
You also have options of running rigid conduit or pouring concrete over it.

> will conduit be needed where the cabling comes up...?
Yes. Dare I ask what this is running to in your garden?

>Are these subject to local codes?
Yes, if any.

Please protect the circuit with a GFCI before it leaves your house.


#2383 - 07/06/01 04:29 PM Re: cable bury depth  
xformer  Offline
Junior Member
Joined: Jul 2001
Posts: 3
Lowell,MI,USA
>Dare I ask what this is running to in your garden?
Well, I had "build a pond" on my "honey do" list, so now I must provide power out to it for the pump.
Thanks for the quick response!
Dave


#2384 - 07/06/01 06:28 PM Re: cable bury depth  
Anonymous
Unregistered

>for the pump.
Your pump should work okay with GFCI.

In case it ever develops a crack, the GFCI can protect anyone who might be wading in the pool or stepping on the pump at the time.

Will the pump be hard-wired or plugged in?
You must use connections, boxes, and covers that are suitable for a wet area while in use. Otherwise, the GFCI will trip when they get wet.


#2385 - 07/06/01 10:28 PM Re: cable bury depth  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
xformer,

Welcome to the Forum.
If you do as DS says and protect your UF cable with a GFCI before going underground you can save yourself a little digging. You'll only need 12 inches of cover by code.

Bill


#2386 - 07/07/01 12:12 AM Re: cable bury depth  
dbc  Offline
Junior Member
Joined: Jul 2001
Posts: 2
Millington
Quote
Originally posted by Bill Addiss:
xformer,

Welcome to the Forum.
If you do as DS says and protect your UF cable with a GFCI before going underground you can save yourself a little digging. You'll only need 12 inches of cover by code.

Bill


I'm sorry if I am not properly responding to this topic but a closer look into the code is in order here. As my company wires over 250 swimming pools a year in a multi-jurisdictional tri-state area a better understanding of direct burial is in order here. NEC 300-5 states that direct buriel i.e. UF cable must be 24" covered not 18". If THHN in PVC conduit is used 18" is permitted. Concrete encasement does diminish this by 6" either way. The exception is only if the circuit is GFCI protected from the panel and not at the pump. The easiest method is to use #12 THNN in IMC or RIDGID conduit where 6" buriel is all that is needed. A foutain pump on 120 requires GFI protection on residential use. If the pump is 240 hard wire it requires no GFI protection on residential usage.


#2387 - 07/07/01 02:17 AM Re: cable bury depth  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
dbc,

Welcome!

Look at column 4 in table 300-5 ('99 NEC)
As per 300-5 in Residential applications 120 volts or less and 20 amp circuit maximum if it is GFCI protected a cover of 12 inches minimum is all that is called for.


Bill

[This message has been edited by Bill Addiss (edited 07-07-2001).]


#2388 - 07/07/01 06:42 AM Re: cable bury depth  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
welcome new posters !

my 2 cnts;

I'm getting a bumper sticker;
'just say no to direct burial'

also, make it THWN for the location

picky, picky, picky...

[Linked Image]


#2389 - 07/07/01 07:11 AM Re: cable bury depth  
xformer  Offline
Junior Member
Joined: Jul 2001
Posts: 3
Lowell,MI,USA
Well, I really started something with this topic, eh? So, now what should I do? I am thoroughly confused. I already have the UF-B 12/2 W/GND cabling and a wet location 2x4 duplex box and was planning on pulling power out of the nearby shed. How about I put GFCI in the shed where I will get my power, then bury the cable 24" and use rigid conduit where cabling enters and leaves the ground? does this sound like an adequate install? By the way, I am really grateful for all of the help on this matter, Thanks to all who have taken the time to read and respond this posting!
Dave


#2390 - 07/07/01 08:57 AM Re: cable bury depth  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
xformer,

It's not a problem. The Book is clear on it.
120v circuit GFCI protected before it goes underground, circuit is 20A or less and it is a Residence. 12 inches is what it says. We do it all the time.

Note: the info above is right out of the Code book, your local inspectors might disagree. You should always check with someone locally to see if there are any local amendments to the code that they recognize.

When in doubt more protection is better.

Bill


Page 1 of 2 1 2

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.8156 MB (Peak: 0.9885 MB) Zlib enabled. Server Time: 2017-07-28 10:54:26 UTC