Does anyone know where I can get a wiring diagram for the old "switched neutral" 3 way wiring?

Work Gear for Electricians and the Trades
Re: Old 3way switched neutrals #23684
03/25/03 07:34 AM
03/25/03 07:34 AM
W
wocolt  Offline
Member
Joined: Dec 2002
Posts: 110
The ones I have seen, the power is at the fixture, and the switchleg is (as it would be normally) but the neutral is switched.
I am sure there are other schemes.

WOC

Re: Old 3way switched neutrals #23685
03/25/03 11:13 AM
03/25/03 11:13 AM
C
CTwireman  Offline
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
Don, are you talking about the old "Chicago" Or Carter system 3 ways?


Peter
Re: Old 3way switched neutrals #23686
03/25/03 03:51 PM
03/25/03 03:51 PM
R
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
I'm not sure what you're looking for, but this is a illegal threeway.

Tie the hot to a traveler terminal, the neutral to a traveler terminal, run the common to the light. Do the same at the other switch. Both commons from each switch go to the light, hot and neutral run between switchs and are tied to the traveler terminals only.

Russ



[This message has been edited by russ m (edited 03-25-2003).]

Re: Old 3way switched neutrals #23687
03/25/03 05:41 PM
03/25/03 05:41 PM
Z
zapped208  Offline
Member
Joined: Feb 2003
Posts: 197
Somewhere in USA
This is what we here in the northeast call a HOT 3-way. Most common place you will find this type of 3-way set up is at dairy farms with a center pole service, and there is a set of floods on the pole and milk house. The 3-ways are fed at the house and from the barn panels. Russ M has the correct wiring of the 3-ways. The 3-ways MUST be fed from the same phase at house and barn. So when working on this type of set up, you must turn off power at house and the barn.


Shoot first, apologize later.....maybe
Re: Old 3way switched neutrals #23688
03/25/03 09:31 PM
03/25/03 09:31 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Don,

I e-mailed you 4 old diagrams out of an old wiring book. See if they can help you. I am not sure if I can post them here on ECN. I might try though.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,515 Are you busy
180,312 Re: Forum
170,808 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.003s) Memory: 0.9735 MB (Peak: 1.1200 MB) Zlib enabled. Server Time: 2018-01-17 03:33:59 UTC