#22545 - 02/24/03 06:16 PM Help With Overhead Temp. Feed  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
In a few days I have to do some work I am not familiar with.

I have to run a Temp 480 Volt 200 Amp (no neutral) feed between two wood poles (typical telephone poles).


1) What is the name of the wedge like clamp that grabs the messenger cable and who makes them?

2) What is the name of the cable is it called triplex? I need 3 hots and messenger/ground.

3) What ampacity table would I use for this?

Any help would be appreciated

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Work Gear for Electricians and the Trades

#22546 - 02/24/03 06:25 PM Re: Help With Overhead Temp. Feed  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,311
1) a deadman is the slang, which my supplier seems to be ok with
2)Quadriplex ,areial rated w/ messenger. now i think what constitutes a 'messenger' is a strand or two of ASCR
3)T310.20 , for NEC, the poco may differ if this is service entrance per se'


#22547 - 02/24/03 11:35 PM Re: Help With Overhead Temp. Feed  
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
1. Some people call them "wedge clamps", or "strain hangers". I've only used them from one manufacturer. The name is "Blackburn".
2. Some advice on cutting quadraplex....don't use your side cutters. There is a hard drawn steel strand in the messenger, and unless you are using 2000 series Kleins, it will ruin your pliers.
3. I agree with Sparky on 310.20.
4. You'll also notice that the insulated conductors have "ribs" on them. The "ribs" are for identification purposes.

Regards,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX

#22548 - 02/24/03 11:47 PM Re: Help With Overhead Temp. Feed  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
ok here is my answer for the temp service :
1) i use it call wedge clamp it make by blackburn compaine it is very common item almost all electral supply centre will have them

2) quadplex BUT one warning for all acsr cables do not use ornaly side cutters it will wreck them in hurry i use specal cutter for ascr simuair to bolt cutter but specical modifation to it and the ascr will be pretty good size steel wire duplex, triplex,and quadplex have them so watch out

3) see nec 310.20 but check poco first

4) tri and quadplex do have rib for identifcation ( you can feel it )

merci marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#22549 - 02/26/03 06:45 PM Re: Help With Overhead Temp. Feed  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
sparky, The Watt Doctor and frenchelectrican

Thank you all for the help the job is done.

You all mentioned the POCO but they were not involved so I looked at 310.20 but ended up going with 4/0 AL as I was adding more length to a long run done in 2/0 AL

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts


Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7686 MB (Peak: 0.9079 MB) Zlib enabled. Server Time: 2017-07-27 20:38:38 UTC