netural and hot reversed? #21984
02/14/03 02:21 PM
02/14/03 02:21 PM
R
rayh78  Offline OP
Member
Joined: Nov 2001
Posts: 23
Used one of the little plug in testers. Test ok on the first outlet of a kitchen circut. the 2nd outlet box shows reversed. Switched white & black wires at outlet and still shows reversed. This should have at least given proper reading. Outlets are ground wire connected and white to large prong opening as required. Very confused?
Also is the only way to test bare cable for hot/netural is to have to connect to a outlet first in order to use a plug in tester. Dosnt seem to be a way with my fluke.
Thanks for any suggestions

Work Gear for Electricians and the Trades
Re: netural and hot reversed? #21985
02/14/03 03:09 PM
02/14/03 03:09 PM
J
JCooper  Offline
Member
Joined: Dec 2002
Posts: 228
Kendall Park, NJ USA
You can use your fluke, put one probe in ground and the other in neutral, should be 0 volts and 0, or close maybe 5 or 10, ohms. Netx probe between neutral and hot, verify voltage, and again between hot and ground.

Re: netural and hot reversed? #21986
02/14/03 04:48 PM
02/14/03 04:48 PM
R
rayh78  Offline OP
Member
Joined: Nov 2001
Posts: 23
Thanks for info on reading fluke.

any idea why it did not work to switch black and white wires on outlet to get a good reading?

Re: netural and hot reversed? #21987
02/14/03 05:09 PM
02/14/03 05:09 PM
T
txsparky  Offline
Member
Joined: May 2001
Posts: 552
Magnolia,.Texas U.S.A.
It's not reversed wiring. If you unplug everything on this circuit, and turn off all switches, your tester will correctly read "open neutral". Somewhere on this circuit, the white wire has become disconnected. This usually happens when a backstab of the white wire becomes loose. You may need to open up every box on the circuit (working or not) and move backstabbed connections to adjacent screws. While you're in there, tighten up any wire nuts. Start with the non-working boxes, and then move to the closest working boxes on the same circuit.


Donnie
Re: netural and hot reversed? #21988
02/15/03 08:28 PM
02/15/03 08:28 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
txsparky,
Good Call, mate, would have said the same thing. [Linked Image]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004