#217383 - 06/28/16 07:07 PM Unique Exhaust Fan Control Request  
Potseal  Offline
Member
Joined: Feb 2013
Posts: 242
Saskatchewan
I have been asked to assist in trying to come up with a method to control an exhaust fan. Currently the exhaust fan is controlled with a typical HOA except it is interlocked with another HOA controller for a supply fan. They want to keep this system intact with the option to control the exhaust fan separately when needed (supply fan would not be running). I'm envisioning a break-before-make rated switch at the supply side that would feed a separate controller for the exhaust fan. As well, I would need a similar switch at the load side to avoid back feeding. Does this sound reasonable? Anyone put together something like this before?


A malfunction at the junction
--------------------------------------
Dwayne

Work Gear for Electricians and the Trades

#217384 - 06/28/16 09:26 PM Re: Unique Exhaust Fan Control Request [Re: Potseal]  
twh  Offline
Member
Joined: Mar 2004
Posts: 919
Regina, Sask.
Use two relays. The first isolates the supply fan interlock and energizes the second relay. The second relay starts the exhaust fan. The second relay should give the necessary delay.


#217385 - 06/29/16 12:33 AM Re: Unique Exhaust Fan Control Request [Re: Potseal]  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,122
Estero,Fl,usa
Put a DPDT relay at the fan so the N/C contacts from the existing controller are isolated when the optional controller takes over on the N/O contacts.


Greg Fretwell

#217386 - 06/29/16 09:22 AM Re: Unique Exhaust Fan Control Request [Re: Potseal]  
ghost307  Offline
Member
Joined: May 2005
Posts: 915
Chicago Illinois USA
Are they really sure that's what they want to do?
The air being exhausted has to come from somewhere.
When you reduce the air supply the exhaust fan won't work quite as well.


Ghost307

#217389 - 07/01/16 11:39 AM Re: Unique Exhaust Fan Control Request [Re: Potseal]  
Potseal  Offline
Member
Joined: Feb 2013
Posts: 242
Saskatchewan
I appreciate the feedback.

Have another idea... What about a simple disconnect on the load side of the supply fan's contactor? The exhaust and supply control circuit's are interlocked which will continue to operate as designed with exception of the supply fan not being energized while the disconnect is open.

Ghost307, I did not provide much information on this matter. The room is at a hospital and is used for isolation. I believe they need the option to run only the exhaust fan while testing the room or something of that nature.


A malfunction at the junction
--------------------------------------
Dwayne

#217390 - 07/02/16 03:33 AM Re: Unique Exhaust Fan Control Request [Re: Potseal]  
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 790
Chicago, Il.
I would work within the existing ladder but don't have enough info as to what's really needed. I take it that both of the switches are normally in the "AUTO" position. You would want to keep any LOTO capability. Does supply AUTO have priority over exhaust AUTO now? Should both AUTOs be able to control the exhaust fan at the same time or do they want a LOCAL/REMOTE AUTO switch? You should ask them for a flow chart. I find ladder design to be fairly easy once folks decide what they actually want. They usually think that they know until you show them that the devil is in the details.
Joe


#217391 - 07/02/16 04:09 AM Re: Unique Exhaust Fan Control Request [Re: Potseal]  
Potseal  Offline
Member
Joined: Feb 2013
Posts: 242
Saskatchewan
Joe, under normal operating conditions both fans are in "auto". There is a small mechanical room located behind the isolation room where the HOA controls are mounted side-by-side on a wall. On occasion there will be a need to run the exhaust fan in "hand" without the supply fan running. This is why I think a simple disconnect to prevent the supply fan from running would suffice. With both fan controls switched to "off" open the disconnect to break the circuit on the load side to the supply fan and then switch both controls to "hand". Once they're done running the exhaust fan switch both controls back to "off", close the disconnect, and then switch back to "auto".


A malfunction at the junction
--------------------------------------
Dwayne

#217392 - 07/02/16 05:28 AM Re: Unique Exhaust Fan Control Request [Re: Potseal]  
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 790
Chicago, Il.
It would seem that you could just have the Exhaust "HAND" position pick a relay with an NC contact, in series with the Supply Fan interlocks. Or you could add a section to the Exhaust selector switch. If they're interlocked, there should already be a warning label about multiple control voltages being present in the cabinet.
Joe



Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 15 (0.003s) Memory: 0.7945 MB (Peak: 0.9597 MB) Zlib enabled. Server Time: 2017-10-18 02:04:03 UTC