Working space in front of elevated busduct system #217136
05/13/16 06:44 PM
05/13/16 06:44 PM
L
LarryC  Offline OP
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Existing warehouse. 2000A service feeding busduct hung off of outside wall. Busduct is 12 feet above floor. All connections from disconnects go up. Owner wants to put workbenches and tool storage cabinets no taller than six feet, below bus, along the wall.

Electrician says no, need to maintain working clearance. I thought the only requirements were 36 inches in front of, six feet or hard ceiling above, and four feet below bottom of disconnect.

Am I completely off base?

Thanks

Work Gear for Electricians and the Trades
Re: Working space in front of elevated busduct system [Re: LarryC] #217148
05/16/16 07:05 AM
05/16/16 07:05 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 926
Chicago Illinois USA
I think the Electrician is correct.
How would you access the bus without moving the cabinets?


Ghost307
Re: Working space in front of elevated busduct system [Re: LarryC] #217151
05/16/16 11:57 AM
05/16/16 11:57 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
What is in the bus duct? Is it something that is "likely to require examination, adjustment, servicing, or maintenance while energized"?

Can they simply put a catwalk over the cabinets? They are 12' AFF. What is the access now?


Greg Fretwell
Re: Working space in front of elevated busduct system [Re: gfretwell] #217152
05/16/16 04:58 PM
05/16/16 04:58 PM
L
LarryC  Offline OP
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Quote
Is it something that is "likely to require examination, adjustment, servicing, or maintenance while energized"?


That was my point. If you have to move or add a disconnect, then move the benches or cabinets at that time. Otherwise the only expected operation while energized would be operating the disconnect via an insulated pole.

Fuse replacement would be done after operating the disconnect and access to the disconnect is easily arranged by step ladder or manlift.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
sparky 22
Admin 20
Potseal 13
Popular Topics(Views)
243,528 Are you busy
180,329 Re: Forum
170,821 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.9584 MB (Peak: 1.0917 MB) Zlib enabled. Server Time: 2018-01-18 00:07:55 UTC