#217136 - 05/13/16 07:44 PM Working space in front of elevated busduct system  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Existing warehouse. 2000A service feeding busduct hung off of outside wall. Busduct is 12 feet above floor. All connections from disconnects go up. Owner wants to put workbenches and tool storage cabinets no taller than six feet, below bus, along the wall.

Electrician says no, need to maintain working clearance. I thought the only requirements were 36 inches in front of, six feet or hard ceiling above, and four feet below bottom of disconnect.

Am I completely off base?

Thanks


Work Gear for Electricians and the Trades

#217148 - 05/16/16 08:05 AM Re: Working space in front of elevated busduct system [Re: LarryC]  
ghost307  Offline
Member
Joined: May 2005
Posts: 906
Chicago Illinois USA
I think the Electrician is correct.
How would you access the bus without moving the cabinets?


Ghost307

#217151 - 05/16/16 12:57 PM Re: Working space in front of elevated busduct system [Re: LarryC]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
What is in the bus duct? Is it something that is "likely to require examination, adjustment, servicing, or maintenance while energized"?

Can they simply put a catwalk over the cabinets? They are 12' AFF. What is the access now?


Greg Fretwell

#217152 - 05/16/16 05:58 PM Re: Working space in front of elevated busduct system [Re: gfretwell]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Quote
Is it something that is "likely to require examination, adjustment, servicing, or maintenance while energized"?


That was my point. If you have to move or add a disconnect, then move the benches or cabinets at that time. Otherwise the only expected operation while energized would be operating the disconnect via an insulated pole.

Fuse replacement would be done after operating the disconnect and access to the disconnect is easily arranged by step ladder or manlift.



Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,707
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.003s) Memory: 0.7603 MB (Peak: 0.8937 MB) Zlib enabled. Server Time: 2017-07-25 16:54:54 UTC