#217079 - 04/29/16 04:12 PM Tracking Live wires .  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 835
Michigan
What do they make that you can trace a wire from Device or Motor to the Panel to get the correct circuit without shutting the power off. Some of the loads run 24/7 And are not marked correctly.
Both 3 phase & single phase.
Thank you
Yoopersup


Work Gear for Electricians and the Trades

#217080 - 04/30/16 02:29 AM Re: Tracking Live wires . [Re: Yoopersup]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
There are breaker finders that insert some kind of signal on the wire that you can pick up with the tester at the breaker end. The one I have is 120v only tho (a wall wart looking sender). I put a 1-15 receptacle on a pigtail with some insulated clips so I can use it on a circuit without a receptacle handy.


Greg Fretwell

#217081 - 04/30/16 11:22 AM Re: Tracking Live wires . [Re: Yoopersup]  
twh  Offline
Member
Joined: Mar 2004
Posts: 922
Regina, Sask.
I tried a couple different tracers that are plugged into an outlet and have had some success and some failures. When I'm turning off a plug circuit that really has to be right, I built a box with a 4 amp cycling load so I can verify the circuit with a clamp-on ammeter.

A telephone toner will work on a dead circuit.


#217082 - 04/30/16 06:36 PM Re: Tracking Live wires . [Re: twh]  
brsele  Offline
Member
Joined: Jul 2008
Posts: 93
Northern Ontario
Originally Posted by twh
I tried a couple different tracers that are plugged into an outlet and have had some success and some failures. When I'm turning off a plug circuit that really has to be right, I built a box with a 4 amp cycling load so I can verify the circuit with a clamp-on ammeter.


So can I ask what do you use for cycling?
I've been looking for one of those flashers people used to use at Christmas, but they don't sell them where I am.

Thanks


#217085 - 05/01/16 01:00 AM Re: Tracking Live wires . [Re: brsele]  
twh  Offline
Member
Joined: Mar 2004
Posts: 922
Regina, Sask.
For a cycling load, I have a couple magnetic heaters inside a 10x10 JB with a heat sink from an old VFD opposite the heaters. They cycle on for about a second and off for about 3 seconds.

It takes about one second for an ammeter to give a good reading. The off time is longer to reduce the heat.

I have an ammeter with forks that slip over the wires so I don't have to clamp on to each wire.

Sometimes the panel feeders have a steady enough load that the phase can be determined, which reduces the number of tests on breakers.

This is a result of an incorrectly labelled breaker that the circuit tracer also incorrectly identified. It's a funny thing. If the power goes out on computers, everyone goes outside for a smoke. If an electrician makes a mistake, they want to see blood on the walls.


#217088 - 05/01/16 12:43 PM Re: Tracking Live wires . [Re: Yoopersup]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
Quote
It's a funny thing. If the power goes out on computers, everyone goes outside for a smoke.


Trust me, when the computers are down, there are still plenty of people who want to see some blood on the wall. wink


Greg Fretwell

#217092 - 05/01/16 10:39 PM Re: Tracking Live wires . [Re: Yoopersup]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 835
Michigan
Most the Loads I am talking about are 3 phase 480 v motor loads.
120 Volt loads are not a problem/
Still Looking



Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.7858 MB (Peak: 0.9424 MB) Zlib enabled. Server Time: 2017-11-23 18:34:22 UTC