#216019 - 09/07/15 08:47 PM 2500 amp service  
Merlin  Offline
Member
Joined: Jan 2004
Posts: 170
NW Indiana
Looking for some suggestions.....I am quoting a job to install a 2500 amp, 480/277V service. This will be feed from a pad mount transformer about 30 feet into a building. Obviously it will be parallel conductor fed. What combination would you all use? 750kcmil, 1000kcmil,.....any thoughts?


Work Gear for Electricians and the Trades

#216020 - 09/07/15 08:56 PM Re: 2500 amp service [Re: Merlin]  
twh  Offline
Member
Joined: Mar 2004
Posts: 905
Regina, Sask.
Aluminum. Then, all sizes are easy.


#216021 - 09/07/15 09:35 PM Re: 2500 amp service [Re: Merlin]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,812
Brick, NJ USA
Merlin:

Common is 6 sets of 600 KCMil Cu THHN/THWN in 4" PVC

You have to check the secondary 'window' of the pad mount xfr., as that limits the quantity of conduits you can install.


John

#216042 - 09/16/15 12:19 AM Re: 2500 amp service [Re: HotLine1]  
Merlin  Offline
Member
Joined: Jan 2004
Posts: 170
NW Indiana
Correct me if I'm wrong, but 6-600's would be
6 x 475 = 2850.
Derated for 4 conductors in conduit(480/277) at 80%
2850 x .8 = 2280.

Wouldn't it be 6x750kcmil?
6 x 535 = 3210
3210 x .8 = 2568


#216045 - 09/16/15 11:35 AM Re: 2500 amp service [Re: Merlin]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,812
Brick, NJ USA
Merlin:
I stand corrected....I did not 'see' 2500 amps.



John

#216073 - 09/22/15 02:10 AM Re: 2500 amp service [Re: Merlin]  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
If this Installation is for Service Feeders (from a Poco Transformer to Service Equipment), you need to verify the requirements with the Service Planner before bidding this Project (or before commencing the actual work!)

If the Installation is on the LOAD side of the Service Disconnect, then (6) 4" Ducts with 4-750MCM CU. per duct is sufficient... if NO Equipment Grounding Conductors are installed!

If an EGC is to be installed, that will be a minimum of (1) 350MCM CU. per duct, so now the Ducts would be 5" (???)
dunno

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!


Member Spotlight
Admin
Admin
NY, USA
Posts: 3,439
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.002s) Memory: 0.7774 MB (Peak: 0.9268 MB) Zlib enabled. Server Time: 2017-05-01 04:29:17 UTC