#21537 - 02/05/03 12:27 AM Receptacle in Closet  
muxx  Offline
Junior Member
Joined: Feb 2003
Posts: 6
Can you put a Receptacle in a small closet? If so, where can it be mounted in a closet.


Work Gear for Electricians and the Trades

#21538 - 02/09/03 02:31 PM Re: Receptacle in Closet  
tsolanto  Offline
Member
Joined: Sep 2002
Posts: 131
Long Island NY
I think its a bad idea if it is a clothes closet but I have never found an article to say you can't

[This message has been edited by tsolanto (edited 02-09-2003).]


#21539 - 02/10/03 02:10 AM Re: Receptacle in Closet  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
ahh for recpetacale in the closet it is a bad idea due few reason
1) hard to get into the rep et plug with all the stuff there.
2) how often any one have one in small closet myself i never see one at all. only very large walk in closet
3) i did check the codes i can't find anything about not useing the rep. in the closest BUT french codes (that where i came from say not allow it in small cloest at all!
i am sure few other electrians will say the same answer what i just spoke above it

merci marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#21540 - 02/10/03 04:19 PM Re: Receptacle in Closet  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Some folks around here have asked for 250V 20A receptacles in their closets, aparently for 1000W metal halides.

[Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#21541 - 02/10/03 06:52 PM Re: Receptacle in Closet  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
'66wv — There will always be regional variations, but way out west, 1kW luminaires in closets would most likely be for year-round, high-yield "herbal" {or "medicinal"} gardening.




[This message has been edited by Bjarney (edited 02-10-2003).]


#21542 - 02/10/03 07:22 PM Re: Receptacle in Closet  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
[Linked Image] [Linked Image] [Linked Image] LOL


Al Hildenbrand

#21543 - 02/10/03 07:29 PM Re: Receptacle in Closet  
ElectricAL  Offline
Member
Joined: Oct 2001
Posts: 597
Minneapolis, MN USA
Muxx,

In addition to '66's observation, there really are good reasons to put receptacles in closets, even a small one. With all the rechargeable batteries in the things we use, having an outlet for the "wall wart transformer" that keeps the cord from going thru the door, is at the top of my list.


Al Hildenbrand

#21544 - 02/10/03 07:45 PM Re: Receptacle in Closet  
Electric Eagle  Offline
Member
Joined: Apr 2002
Posts: 914
Alpharetta, GA
We do it all the time in walk in closet for a variety of reasons, ironing board, towel warmer, battery charger. Small closets get them all the time also, primarily for the security system xfrmr. To the best of my knowledge there's nothing in the NEC that prohibits this. If there is, the inspectors in my area don't seem to know it either.

[This message has been edited by Electric Eagle (edited 02-10-2003).]


#21545 - 02/10/03 08:33 PM Re: Receptacle in Closet  
lighthouse  Offline
Member
Joined: Jan 2003
Posts: 134
philadelphia pa 19125
joe...you did it to me again [Linked Image] lol

[This message has been edited by lighthouse (edited 02-10-2003).]


#21546 - 02/11/03 07:41 AM Re: Receptacle in Closet  
tsolanto  Offline
Member
Joined: Sep 2002
Posts: 131
Long Island NY
Are you concerned about clothes coming in contact with the receptacles. What happens if the plug is not in all the way and clothes come in contact with it... Seems like a bad idea to me.


Page 1 of 3 1 2 3

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.002s) Memory: 0.8177 MB (Peak: 0.9935 MB) Zlib enabled. Server Time: 2017-07-26 04:49:17 UTC