#215284 - 04/04/15 12:19 AM MC cable protection  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
1. Can MC cable be run down a cement wall to a receptacle in a residential basement?
2. Can you connect a furnace circuit to a furnace in a residential home by dropping down with MC cable from a box in the ceiling where it is spliced to NM cable?
3. If the answer is no, what are the code reference?
4. Subject to physical damage? If so, how do you protect it?

Last edited by George Little; 04/04/15 12:21 AM. Reason: changed bad wording.

George Little

2017 / 2014 NEC & Related Books and Study Guides

#215286 - 04/04/15 03:43 AM Re: MC cable protection [Re: George Little]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
This is the old "physical damage" question and most AHJs have their own opinion of what it really is.
Some places will allow NM on running boards down to some arbitrary height above FF. Others want EMT. Most are somewhere in between (Smurf, MC/AC etc)
It really comes back to how exposed it is to physical damage and is that damage "severe"?
I am one of those middle guys. A metallic cable, Greenfield or smurf would work for most of these cases. I never thought much of Romex on running boards, particularly much below 6'6 but that was the law of the land in Maryland when I was there, down to about 48" or even 36".


Greg Fretwell

#215296 - 04/04/15 04:02 PM Re: MC cable protection [Re: George Little]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
George:
By your numbers:

1: Unless physical damage is evident, I see no reason that it is not compliant. No, I have not seen anyone doing this around here. Professionals use a raceway. (EMT/PVC/etc)

2: Yes. As long as the MC is supported, and not subject to physical damage.

4: Protection by a raceway (EMT/PVC, etc) or any other suitable (to the AHJ) method I would guess.


John

#215314 - 04/07/15 11:44 AM Re: MC cable protection [Re: George Little]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 830
Michigan
George
I'd say use PVC sch 80 for protection when subject to physical harm. (no bonding worries).
Example : underground coming up a outside pole.
Yoopersup




Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.003s) Memory: 0.7608 MB (Peak: 0.8942 MB) Zlib enabled. Server Time: 2017-10-19 10:54:54 UTC