#214757 - 01/21/15 01:59 PM Wall Mounted Oven 4.1KW  
SparksFlying  Offline
New Member
Joined: Oct 2014
Posts: 6
Austin, Texas
What size breaker and what size cable should be used.


Tools for Electricians:

#214758 - 01/21/15 05:48 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,122
Estero,Fl,usa
Sounds like 10ga/30a to me. What do the instructions say?
A lot of times they say 8ga/40a no matter what oven is installed.


Greg Fretwell

#214786 - 01/24/15 01:24 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
4100 VA / 240V = 17.0833333- Amps

As Greg has mentioned, #8 THHN CU. protected by a 40 Amp 2 Pole Breaker is "The Norm".

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#214791 - 01/24/15 03:45 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,122
Estero,Fl,usa
It would probably live forever on 12ga and 20a breaker, even with the timer and the light inside but you should still be sizing at 125% of the calculated current. That is how I got to 10ga/30a.


Greg Fretwell

#214812 - 01/26/15 03:49 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
SparksFlying  Offline
New Member
Joined: Oct 2014
Posts: 6
Austin, Texas
Yes they only call for a 20ga and 20amp breaker but we are going with a 10ga/30amp and sleep well...'

Thanks



Member Spotlight
Admin
Admin
NY, USA
Posts: 3,458
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.7679 MB (Peak: 0.9088 MB) Zlib enabled. Server Time: 2017-10-18 23:57:37 UTC