ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 3
Recent Posts
Nec circuit protection
by gfretwell. 11/21/17 11:01 PM
FPE in Germany
by Texas_Ranger. 11/19/17 07:30 AM
Ceiling fan distance from outdoor hot tub
by gfretwell. 11/16/17 02:18 AM
diazed fuses
by Texas_Ranger. 11/13/17 03:02 PM
Theft deterrent alarm
by gfretwell. 11/12/17 01:39 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
242,614 Are you busy
178,812 Re: Forum
170,052 Need opinion
Who's Online Now
0 registered members (), 20 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#214757 - 01/21/15 12:59 PM Wall Mounted Oven 4.1KW  
SparksFlying  Offline
New Member
Joined: Oct 2014
Posts: 6
Austin, Texas
What size breaker and what size cable should be used.


Tools for Electricians:

#214758 - 01/21/15 04:48 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
Sounds like 10ga/30a to me. What do the instructions say?
A lot of times they say 8ga/40a no matter what oven is installed.


Greg Fretwell

#214786 - 01/24/15 12:24 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
4100 VA / 240V = 17.0833333- Amps

As Greg has mentioned, #8 THHN CU. protected by a 40 Amp 2 Pole Breaker is "The Norm".

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#214791 - 01/24/15 02:45 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
It would probably live forever on 12ga and 20a breaker, even with the timer and the light inside but you should still be sizing at 125% of the calculated current. That is how I got to 10ga/30a.


Greg Fretwell

#214812 - 01/26/15 02:49 PM Re: Wall Mounted Oven 4.1KW [Re: SparksFlying]  
SparksFlying  Offline
New Member
Joined: Oct 2014
Posts: 6
Austin, Texas
Yes they only call for a 20ga and 20amp breaker but we are going with a 10ga/30amp and sleep well...'

Thanks



Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 15 (0.003s) Memory: 0.7678 MB (Peak: 0.9087 MB) Zlib enabled. Server Time: 2017-11-22 14:40:00 UTC