#214531 - 12/18/14 11:28 PM derating rooftop conductors  
BigB  Offline
Member
Joined: Mar 2004
Posts: 719
Tucson, AZ USA
When derating THWN-2 copper conductors for ambient that will eventually terminate in a sub panel with a 125 amp rating can I use the 90C column?


2017 / 2014 NEC & Related Books and Study Guides

#214533 - 12/19/14 04:54 AM Re: derating rooftop conductors [Re: BigB]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
The sole and only reason for that column IS derating.

For there are no 90 degree rated devices out there.

One then uses the lesser computed ampacity limit.

So, yes, you start with the 90 degree column.


Tesla


Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 15 (0.002s) Memory: 0.7427 MB (Peak: 0.8584 MB) Zlib enabled. Server Time: 2017-05-25 23:46:45 UTC