Rate Thread
derating rooftop conductors #214531
12/18/14 10:28 PM
12/18/14 10:28 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 721
Tucson, AZ USA
When derating THWN-2 copper conductors for ambient that will eventually terminate in a sub panel with a 125 amp rating can I use the 90C column?

2017 / 2014 NEC & Related Books and Study Guides
Re: derating rooftop conductors [Re: BigB] #214533
12/19/14 03:54 AM
12/19/14 03:54 AM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
The sole and only reason for that column IS derating.

For there are no 90 degree rated devices out there.

One then uses the lesser computed ampacity limit.

So, yes, you start with the 90 degree column.


Tesla

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,599 Are you busy
180,406 Re: Forum
170,869 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 15 (0.003s) Memory: 0.9405 MB (Peak: 1.0584 MB) Zlib enabled. Server Time: 2018-01-23 15:38:48 UTC