US Fuse Sizes #21445
02/02/03 11:47 PM
02/02/03 11:47 PM
Trumpy  Offline
OP
Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Just wondering, is there a standard progression in the sizes of fuses/CB's in the US.
How would you protect each size/type of cable available to you?.
Would this vary between a Domestic or Commer-
cial or Industrial Installation?.
How are fuses that protect Motors, sized?.
Your help would be most appreciated.

Work Gear for Electricians and the Trades
Re: US Fuse Sizes #21446
02/03/03 06:53 AM
02/03/03 06:53 AM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
The NEC lists standard fuse & circuit breaker sizes (Article 240.6).
I'm sure someone here can download the article.
Generally, fuses that protect motors can be sized up to 300% for Nontime-delay and 175% for Time-delay. (Table 430.52)
There are exceptions to these rules.

Re: US Fuse Sizes #21447
02/04/03 10:06 PM
02/04/03 10:06 PM
Trumpy  Offline
OP
Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Thanks, Redsy. [Linked Image]

Re: US Fuse Sizes #21448
02/05/03 07:46 PM
02/05/03 07:46 PM
P
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Quote
240.6 Standard Ampere Ratings

(A) Fuses and Fixed-Trip Circuit Breakers. The standard ampere ratings for fuses and inverse time circuit breakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50, 60, 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300, 350, 400, 450, 500, 600, 700, 800, 1000, 1200, 1600, 2000, 2500, 3000, 4000, 5000, and 6000 amperes. Additional standard ampere ratings for fuses shall be 1, 3, 6, 10, and 601. The use of fuses and inverse time circuit breakers with nonstandard ampere ratings shall be permitted.

I seem to recall a thread a few months ago discussing the reason for the peculiar 601A rating, although I can't remember the explanation.



[This message has been edited by pauluk (edited 02-05-2003).]

Re: US Fuse Sizes #21449
02/05/03 10:32 PM
02/05/03 10:32 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,919
Brick, NJ USA
Trumpy:
I see Paul UK beat me to posting the table.
Residential is mostly circuit breakers nowadays. You may see fuses at the central AC condenser IF the mfg spec's FUSES, if not it's a HACR rated CB. There are still some edison (plug) fuses in old homes, and some cartridge fuse main service discos around.

Commercial and industrial lighting and GP circuits are also CB's. Fuses for motors and equipment. Fuses are a preferred OCP where a high AIC rating is required, as the high AIC rated CB's are very pricey.

OCP (overcurrent protection) for cables is based on the NEC; Tables 310-16 to 310-86 of the '99 NEC. If you would like a copy of the tables, e-mail me your address, and I will mail you them.

Hope the above helps
John


John
Re: US Fuse Sizes #21450
02/07/03 08:40 PM
02/07/03 08:40 PM
Trumpy  Offline
OP
Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Paul,
Thanks for posting them fuse sizes, I never
really thought that so many sizes of fuses,
were available.
I also realise that CB's make up this list too.
Hotline,
Thanks for the back-up info, too, most appreciated!. [Linked Image]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,597 Are you busy
180,402 Re: Forum
170,868 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9762 MB (Peak: 1.1228 MB) Zlib enabled. Server Time: 2018-01-23 09:49:29 UTC