#214327 - 11/16/14 02:45 PM NM Cable entering boxes.  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
The question came to me about how far must the NM cable sheath enter the boxes? I could only find the information located in 334.15(C). Nothing about entering the box sans the conduit. My answer would be, the sheath must extend beyond the clamping device be it a non-metallic box or a metal one. The person calling me was concerned because his boss wants the sheath to be at least 3/4" into the box.
There's got to be more important things than this dispute.


George Little

2017 / 2014 NEC & Related Books and Study Guides

#214329 - 11/16/14 08:32 PM Re: NM Cable entering boxes. [Re: George Little]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,864
Brick, NJ USA
George:
From 314.17 (C) of 2014 NEC.....

Where nonmetallic sheathed cable or multi-conductor Type UF cable is used, the sheath shall extend not less than 6 mm (1/4 in.) inside the box and beyond any cable clamp. In all instances, all permitted wiring methods shall be secured to the boxes.


Last edited by HotLine1; 11/17/14 11:04 AM. Reason: Corrected copy booboo

John

#214331 - 11/17/14 03:44 AM Re: NM Cable entering boxes. [Re: George Little]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,118
Estero,Fl,usa
1/4" in english


Greg Fretwell

#214333 - 11/17/14 05:10 PM Re: NM Cable entering boxes. [Re: George Little]  
ghost307  Offline
Member
Joined: May 2005
Posts: 911
Chicago Illinois USA
Yep, 1/4" minimum.


Ghost307

#214335 - 11/17/14 07:45 PM Re: NM Cable entering boxes. [Re: George Little]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Thanks Guys. You are the best. I would have expected it to be in Article 334 but it wasn't. HEY Inspectors have every right to be wrong :)) And I'm probably one of the few that would admit it.

That's what this BB is all about.


George Little

#214336 - 11/17/14 10:50 PM Re: NM Cable entering boxes. [Re: George Little]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,864
Brick, NJ USA
George:
As I say to some..."I'm human, I do make mistakes too"


John

#214339 - 11/18/14 12:20 AM Re: NM Cable entering boxes. [Re: George Little]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,118
Estero,Fl,usa
I guess it is because there is more than one kind of cable and they were trying to avoid the mess that was created when they put a cable rule in 320 and referred to it in all the other cable articles. (like accessible attics in 330.23 334.23 etc)


Greg Fretwell


Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.030s Queries: 15 (0.003s) Memory: 0.7853 MB (Peak: 0.9427 MB) Zlib enabled. Server Time: 2017-09-26 12:53:31 UTC