35mm 5 conductor cable distance to 50Kva xfromer #214127
10/09/14 05:10 AM
10/09/14 05:10 AM
P
PN1  Offline OP
New Member
Joined: Oct 2014
Posts: 5
Camp Arifjan Kuwait
Gentlemen
I have an installation where i have a 125Amp MCCB to a 50Kva transformer. My cable size is 35MM. The distance of the conductor is approximately 300 feet. My question is. Is the 35MM(2/0 conductor of the right size for the distance of the cable run. Insight will be most appreciated.

Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: 35mm 5 conductor cable distance to 50Kva xfromer [Re: PN1] #214128
10/09/14 10:58 AM
10/09/14 10:58 AM
T
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,409
Vienna, Austria
Gut reaction: no.

Reasoning: while tables do vary, we can safely assume that the rating of copper wires is roughly the same around the world. According to the Austrian table, 35 mm2 is only good for 119 amps if there are three current carrying conductors (i.e. a 3-phase system, the neutral is not considered a current-carrying conductor in this case, only in single phase applications) and at 30 C ambient temperature. At 25 C we can go up to 128 amps but considering you're in Kuwait I seriously doubt you would get by without exceeding that temperature even if the cable is run underground. Sooo, even without doing any voltage drop calcs it's at the very best borderline.

I quickly did an online voltage drop calculation and that read 1.9%. Way too much for a main feeder, you'd want more like 0.5% for anything close to European standards (most European countries specify no more than 4% in the entire fixed installation).

Unless this is a "make do" situation definitely upgrade to 50 mm2 or downgrade to 100 A or smaller MCCB (and even that results in a rather bad 1.5% voltage drop).

Re: 35mm 5 conductor cable distance to 50Kva xfromer [Re: PN1] #214132
10/09/14 09:03 PM
10/09/14 09:03 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Temperature de-rating is a major concern.

In Las Vegas, Nevada, USA, everything has to be up-sized -- and the authorities want every conductor above ground whenever this is at all practical.

In Kuwait it has to be a hot as Las Vegas. You have to design for the heat -- worst case.

So it's also important to use insulation that has the highest temperature rating that's financiall viable. (It being understood that MI is totally impractical.)

The last time I looked cross-linked polyethylene was the favored insulation. ( XHHW-2 for Americans )

I would expect that the local trade has already resolved the insulation type for your climate.

BTW, 125A for a 50kVA transformer doesn't add up.

I'm suspicious that your climate forces everyone to use oversized thermal circuit breakers. You may be running far fewer amps than us temperate climate electricians are used to.

Without actually knowing your loading (amps & volts) I hesitate to run the numbers.



Tesla
Re: 35mm 5 conductor cable distance to 50Kva xfromer [Re: Tesla] #214147
10/14/14 05:36 AM
10/14/14 05:36 AM
P
PN1  Offline OP
New Member
Joined: Oct 2014
Posts: 5
Camp Arifjan Kuwait
Thanks for the insight. The cable is rated to 50cecius. Originally I wanted to use a 30Kva transformer but out here it is near impossible to locally find step dowen transformers from british to american voltage. Again thank you.

V/r.

PN1

Re: 35mm 5 conductor cable distance to 50Kva xfromer [Re: PN1] #214149
10/14/14 01:24 PM
10/14/14 01:24 PM
T
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,409
Vienna, Austria
50 C conductor temperature?!? That'll force you to derate even further!

Is your MCCB supposed to protect the transformer? Then I'd say start by sizing that appropriately and then calculate cable size etc.

Re: 35mm 5 conductor cable distance to 50Kva xfromer [Re: PN1] #214626
12/27/14 07:02 PM
12/27/14 07:02 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Umm,
What voltage is this system?


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,583 Are you busy
180,379 Re: Forum
170,856 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 15 (0.005s) Memory: 0.9759 MB (Peak: 1.1242 MB) Zlib enabled. Server Time: 2018-01-21 22:33:42 UTC