#214000 - 09/18/14 05:54 PM fire pump service disconnect  
cgw  Offline
Member
Joined: Jul 2004
Posts: 133
Rochester NY
Is it OK to have a fire pump main service disconnect then feeder to the fire pump controller which has it's own disconnect?
Too many disconnects.
In this case the fire pump is far from the electric service (>350'). The fire pump service entrance could be run all the way to the fire pump room. However the standby generator is located at the electric service so it makes much more sense to put the main disconnect and transfer switch near the electric service (and generator) and run a feeder to the fire pump controller.


2017 / 2014 NEC & Related Books and Study Guides

#214002 - 09/19/14 10:01 AM Re: fire pump service disconnect [Re: cgw]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,826
Brick, NJ USA
It will be best to check with the design professional for the project, and the local AHJs, both Electrical and Fire

Read thru 695.4 (B) (1). IMHO, there are too many variables to say yes or no to your situation.



John

#214005 - 09/20/14 09:45 AM Re: fire pump service disconnect [Re: cgw]  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
I see nothing in the NEC that would prevent you from having two disconnects, in series, for a fire pump installation.
I have designed, and had installed, new disconnects with short circuit protection upstream from existing fire pump services. They have not been questioned by the AHJ.



Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.003s) Memory: 0.7520 MB (Peak: 0.8781 MB) Zlib enabled. Server Time: 2017-05-29 17:11:28 UTC