ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
Feed to spa panel
by HotLine1. 06/25/17 05:28 PM
Weatherhead, POA, height?
by HotLine1. 06/24/17 02:37 PM
Windows 7 update problem
by ampherder. 06/21/17 07:01 AM
Norwegian power?
by dsk. 06/19/17 03:40 PM
Anyone ever take a Furnas A14D drum sw apart?
by gfretwell. 06/17/17 08:14 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
238,233 Are you busy
173,445 Re: Forum
166,253 Need opinion
Who's Online Now
0 registered members (), 47 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#213825 - 08/02/14 11:48 AM Label or the manual  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
An interesting issue came up over on one of the Usenet groups

There is a Sea Breeze mini split air conditioner that has an installation manual that says it should be connected with 6 gauge copper. The label says "minimum circuit ampacity" is 26 amps. So who do you believe?
The breaker size is 50a.
http://www.irproducts.biz/documents/SB-NewMultiZone.pdf


Greg Fretwell

Work Gear for Electricians and the Trades

#213826 - 08/02/14 12:19 PM Re: Label or the manual [Re: gfretwell]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,833
Brick, NJ USA
Greg:
Well, in the real world....the nameplate wins. I would rarely see an install manual; I would ask for it if I had a question, and hope the HO had it.

They may have sized the branch circuit based on the OCP?



John

#213827 - 08/02/14 01:11 PM Re: Label or the manual [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
Quote
They may have sized the branch circuit based on the OCP?



Clearly that is what happened. ... in the 60c column


Greg Fretwell

#213829 - 08/03/14 01:57 AM Re: Label or the manual [Re: gfretwell]  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
Curiosity query...

What was the Intensity level of Flames emitted (by the Usenet Members), when the reply Message stating:
"#10 THW Cu. is Adequate and Compliant"
was posted to the Thread???
laugh yay rolleyes bash

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#213830 - 08/03/14 02:04 AM Re: Label or the manual [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
One guy in particular still will not let it go.

They are off on a "continuous load" side track now.
I tried to explain that motor circuits already have the 125% of FLA requirement and this would be part of the minimum ampacity calculation.

I explained I would trust the engineer who did that calculation more than a tech writer who might not have English as his first language.


Greg Fretwell

#213844 - 08/11/14 08:28 PM Re: Label or the manual [Re: gfretwell]  
anothermarty  Offline
New Member
Joined: Feb 2006
Posts: 3
MA
Label for outdoor unit only... all the inside coils grab power from the outdoor unit.

Now why its ok to use 14/3 or4 between inside and outside can start another argument smile


#213845 - 08/11/14 10:54 PM Re: Label or the manual [Re: gfretwell]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,833
Brick, NJ USA
Correct me if this is wrong....
The inside unit (fan coil) is fed from the outside unit (condenser) and there is factory OCP for the fan coil feed within the condenser.

Most of the units I have seen have 'factory' wiring from the Cu to the FC.



John

#213846 - 08/12/14 01:15 AM Re: Label or the manual [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
I have 2 of these mini splits and one the inside units runs on low voltage that could be run with bell wire Spec'ed as thermostat cable. It is a very small load (a little fan and an electronic board).
The other uses line voltage but just at a few amps.


Greg Fretwell

#213847 - 08/12/14 02:06 AM Re: Label or the manual [Re: gfretwell]  
anothermarty  Offline
New Member
Joined: Feb 2006
Posts: 3
MA
A few amps x 4-5 inside line voltage coils adds up Read the specs 3.5x up to 5 so about 17 amps total inside plus 26 out 50 amps seems right



#213848 - 08/12/14 01:01 PM Re: Label or the manual [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
The conductors going to each inside unit only carry the current to that unit. That is why they can be #14.
As for the outside unit, that is specified on the label and you have to trust the engineer who computed it.


Greg Fretwell


Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.8122 MB (Peak: 0.9927 MB) Zlib enabled. Server Time: 2017-06-26 12:10:58 UTC