UV heaters #213535
05/29/14 07:25 PM
05/29/14 07:25 PM
S
schenimann  Offline OP
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
I have a job next week wiring a UV heater for a printing press. The heater is rated at 80 amps. I have never messed with these before. Do I need to upsize my breaker at all or does it get wired as it is rated? It is 240v 3ph. I don't do much 3ph work so this is a little out of my league.

Work Gear for Electricians and the Trades
Re: UV heaters [Re: schenimann] #213537
05/29/14 09:39 PM
05/29/14 09:39 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
For such exotic gear -- call their tech rep.

They may have pdf on the Web.

UV 'heaters' doesn't quite sound right. I strongly suspect that these are intermittent loads -- kind of like a Xerox machine.

BTW, 240VAC 3 phase is now an uncommon Service. They may have an associated 3 phase autoformer to boost 208Y120 up to the machine's requirement.

Is there any chance that this gadget is a component of their lithographic process?


Tesla
Re: UV heaters [Re: schenimann] #213541
05/29/14 10:19 PM
05/29/14 10:19 PM
S
schenimann  Offline OP
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
UV heater is not quite right. It is actually UV bulbs for a drying process in their flexographic printing process. They currently have a 240VAC 3 phase service that we installed the 240VAC service about 7 years ago. I worked for my dad at the time so I'm not sure exactly why. Something with the POCO and available power in a rural residential area. He is haveing the equipment wired for this voltage.

I will call the tech rep. That is a good idea.

Re: UV heaters [Re: schenimann] #213543
05/29/14 11:42 PM
05/29/14 11:42 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,165
Estero,Fl,usa
80a?
One single phase? 19.2KW element?
Or are there multiple elements spread across the phases?
Either way,
That is a heluva heater.



Greg Fretwell
Re: UV heaters [Re: schenimann] #213555
06/01/14 11:26 AM
06/01/14 11:26 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
All the UV heaters (printing) I have come upon had a control panel that the feeder connected to, and the circuits feeding the individual lamp stations were 'factory' from the controller.

Ususl practice was to install the feeder to the MOCP on the controller nameplate.


John
Re: UV heaters [Re: schenimann] #213557
06/01/14 07:12 PM
06/01/14 07:12 PM
W
WESTUPLACE  Offline
Member
Joined: Mar 2004
Posts: 251
Kingwood, TX USA
I install and work on these all the time. They are also used in the screen printing business. Most rated at 80 amps will be served by a 100 amp service, but always go on the name plate rating. A disconnect should be installed at the machine. BTW 240v 3ph service is the norm here in Houston TX.

Re: UV heaters [Re: schenimann] #213572
06/04/14 10:28 AM
06/04/14 10:28 AM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
I have also dealt with UV Dryers, along with UV Ovens, in several Design-Build Projects (mostly on the "Design" side of the Projects).
The Lamps on a few "Older" UV Dryers were similar to the High Pressure Mercury HID Type Lamps used in 10KW Tanning Beds (Quartz Envelopes with fixed Conductor Leads).

As described by others in this Thread, refer to the Equipment's Nameplate FLA (or better yet, MCA), and design the Branch Circuit from the Load indicated per Nameplate.

Sidenote: Having a 240V 3 Phase Delta System available from the Utility, is so nice to have at the Service Equipment, when the Client's Equipment is rated 230-240VAC 3 Phase.
Otherwise, such Equipment is connected to an SDS (Transformer with 240V 3 Phase Delta Secondary), and that SDS is either Corner Grounded or Center-Tap Grounded. I prefer Center-Tap Grounding.

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,916
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 24
Admin 19
Potseal 13
Popular Topics(Views)
243,510 Are you busy
180,295 Re: Forum
170,799 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 15 (0.003s) Memory: 0.9850 MB (Peak: 1.1425 MB) Zlib enabled. Server Time: 2018-01-16 11:35:40 UTC