#213358 - 04/15/14 02:38 PM LED tube wiring Disconnect required?  
rmiell  Offline
Member
Joined: Nov 2000
Posts: 242
La Junta, Co. USA
According to NEC 2014, Section 410.130(G)(1), fluorescent luminaires with ballasts are required to have a disconnecting means either internal or external to each luminaire.

How about when the ballast is unwired (or removed) in order to install self-driven LED tubes, in which the 120v (or 277v) branch circuit is wired directly to the socket on one end of the fixture?

Should this be a code requirement, or not?

I think this requirement was put in to address the changing out of ballasts, so you did not need to turn off the switch/breaker feeding the whole row of recessed trouffers. I think that there may be a need to disconnect the incoming power if a socket goes bad, but not necessarily when a tube goes bad, so the same thinking should apply.

Thoughts?

Rick Miell


2017 / 2014 NEC & Related Books and Study Guides

#213361 - 04/15/14 08:41 PM Re: LED tube wiring Disconnect required? [Re: rmiell]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,858
Brick, NJ USA
In the 'old days'the ballast disconnect was either the cutter on a T-stripper, or opening a 'hot' splice.

The requirement for the quick disco on replacement ballasts, and new fixtures IMHO is a 'good idea'.

With the quickly changing LED items, the NEChas to play catch-up.



John

#213365 - 04/15/14 10:41 PM Re: LED tube wiring Disconnect required? [Re: rmiell]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
The irony is that the NEC is pressing the installation of disconnecting means at a time when it will be decades between service calls.

Too late!

IMHO, the Code should discourage 480VAC line to line voltages for illumination. 277VAC line to neutral ought to be the upper limit. This would reduce the size of any arcs.

Now that LED is sweeping the market, there is reduced need for watts.

Additionally, ganging contactor neutrals under one wire nut ought to be discouraged. Such lighting control cabinets should have isolated neutral bars, instead. Why?

It then becomes possible to un-circuit a contactor during production hours without hazarding ungrounded electronic ballasts. A broken return is brutal on electronics. It's a nasty shock risk for the service electrician. A cheesy isolated neutral rail is a trivial expense to stop the problem.

(I've seen control cabinets with no less than 12 neutrals in #12 stuffed into big blue wire nut pairs. With a jumper linking them. The amps were no biggie. The complications while the system was up and running ( a 24hr shop ) made it a nightmare.





Tesla

#213366 - 04/15/14 10:46 PM Re: LED tube wiring Disconnect required? [Re: rmiell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,103
Estero,Fl,usa
I would not be surprised if they did not extend this to any active component of a commercial luminaire. The LEDs may last longer than ballasts but they are likely to still be replaced hot.

This is where I would rather see NEMA step up and come up with a standard connector for ballasts or any other follow on technology.

I am not sure why it couldn't just be the good old 5-15, 6-15 and 7-15. Then you are voltage identifying and standard.


Greg Fretwell


Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 15 (0.003s) Memory: 0.7621 MB (Peak: 0.8958 MB) Zlib enabled. Server Time: 2017-08-22 01:55:14 UTC