ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
Feed to spa panel
by gfretwell. 06/24/17 10:22 PM
Weatherhead, POA, height?
by HotLine1. 06/24/17 02:37 PM
Windows 7 update problem
by ampherder. 06/21/17 07:01 AM
Norwegian power?
by dsk. 06/19/17 03:40 PM
Anyone ever take a Furnas A14D drum sw apart?
by gfretwell. 06/17/17 08:14 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
238,208 Are you busy
173,420 Re: Forum
166,235 Need opinion
Who's Online Now
0 registered members (), 45 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#213180 - 03/27/14 08:43 PM Bare Copper In Raceway  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 216
Washington...Not DC
I went to look at a job, where some copper thieves stole the parking lot light control wires, from a church none the less.
I discovered the ground wire pulled with the home run is bare copper, which I thought was against code in a raceway. Am I right? Or was this another myth I believed in? Also what do you think about split bolting the 3 control wires and heat shrinking them in each hand hole? $50 a pop for the resin kits seems kinda pricing, when split bolts/heat shrink work just fine.

Thanks, H20

Last edited by watersparkfalls; 03/27/14 08:45 PM.

2017 / 2014 NEC & Related Books and Study Guides

#213181 - 03/27/14 09:47 PM Re: Bare Copper In Raceway [Re: watersparkfalls]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
I don't work the traffic and signals market...

But the last NEC/ IBEW job I saw used bare #10 solid as the grounding conductor inside PVC for street illumination. It appeared that they used 1 1/4" as their minimum conduit size.

I was kind of jealous, they had an entire 20-foot double axle trailer dedicated to holding their conductor selections. I could never get such a rig to roll around our big box slabs.

That's the only contractor I can recall using bare grounding conductors -- excluding bare solid grounding electrode conductors.


Tesla

#213182 - 03/27/14 09:54 PM Re: Bare Copper In Raceway [Re: watersparkfalls]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
The only restriction I know that might affect that is that 8ga or larger solid is not allowed in a raceway.
The only exception I can think of is a GEC.

Quote
310.3 Stranded Conductors.
Where installed in raceways, conductors of size 8 AWG and larger shall be stranded.
Exception: As permitted or required elsewhere in this Code.


Greg Fretwell

#213185 - 03/28/14 10:54 AM Re: Bare Copper In Raceway [Re: watersparkfalls]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,832
Brick, NJ USA
H2o:
No issue with the bare to my knowledge as Greg said.

Now, the split bolt issue. Do you mean 3 control conductors, or you have to put 3 into a split bolt?
Most, if not all split bolts are only listed/labeled (your choice) for two (2) conductors. ie; run/tap. Your AHJ may have an issue with 3 conductors.





John

#213190 - 03/28/14 03:19 PM Re: Bare Copper In Raceway [Re: watersparkfalls]  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 216
Washington...Not DC
HotLine I was going to put all 3 control wires in the split bolt, NSI industries claim to have a listed split bolt for 3 copper wires. However I am leaning towards Ideals blue weatherproof wirenuts, they are rated for wet locations and my connections are in a hand hole, so might truly be the safest and cost effective way to reconnect lights. Need to secure hand holes from future thefts any thoughts on how to? Was thinking drilling and tapping, but that diamond plate is thick.

Not sure where I got it in my head "no bare in raceway" however I will double check my WAC(Washington Administrative Code)book, however if previous installer was signed off, must be fine.

Thanks,
H20


#213191 - 03/28/14 03:50 PM Re: Bare Copper In Raceway [Re: watersparkfalls]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,832
Brick, NJ USA
The Ideal big blues sound like a plan.


John

#213204 - 03/29/14 03:02 PM Re: Bare Copper In Raceway [Re: watersparkfalls]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,326
Alaska
Bare copper ground in a conduit is not a code issue spec issue perhaps but not a code issue.

As for the split bolts/resin question. That depends on the "engineer" of the project. If done right, split bolt/resin is definently bullet proof for a long tern installation. Way better then wire nuts given their location. If no rework or add to later is not in the cards, bullet proof is a definent plus if the customers are willing to pay for it.


"Live Awesome!" - Kevin Carosa


Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.7869 MB (Peak: 0.9428 MB) Zlib enabled. Server Time: 2017-06-25 12:13:15 UTC