No Way!! #213021
03/07/14 09:33 PM
03/07/14 09:33 PM
Trumpy  Offline
OP
Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Guys,
Have a look at this install of a main breaker in a building.
I would tend to hope this failed an inspection.

[Linked Image]

Hey, at least he got the colours around the right way. rolleyes

Tools for Electricians:
Re: No Way!! [Re: Trumpy] #213022
03/07/14 09:50 PM
03/07/14 09:50 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Interesting!! Long studs to help with the alignment, & reduce the bends required in the conductor??

Why the black tape around the white(center) conductor?


John
Re: No Way!! [Re: Trumpy] #213023
03/07/14 09:50 PM
03/07/14 09:50 PM
M
mbhydro  Offline
Member
Joined: Feb 2003
Posts: 349
Winnipeg MB Canada
Saves time feeding the wire back to the bus bars.

Is that a factory wire job on the main (looks nice with the heat shrink tube) or did somebody in the field cut them to short as I have never seen a panel like that in Canada.

Re: No Way!! [Re: Trumpy] #213024
03/07/14 10:16 PM
03/07/14 10:16 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Let's see ...

Steel bolts that are smaller in diameter than the better conductors that are much larger in diameter.

Looks like three M8 steel fusable links.

grin

Re: No Way!! [Re: HotLine1] #213026
03/07/14 10:59 PM
03/07/14 10:59 PM
Trumpy  Offline
OP
Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Originally Posted by HotLine1

Why the black tape around the white(center) conductor?

John,
That isn't tape, it's just a poor heatshrinking job.

Re: No Way!! [Re: mbhydro] #213027
03/07/14 11:14 PM
03/07/14 11:14 PM
Trumpy  Offline
OP
Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Originally Posted by mbhydro

Is that a factory wire job on the main (looks nice with the heat shrink tube) or did somebody in the field cut them to short as I have never seen a panel like that in Canada.

What caused this to happen is the breaker should have been mounted down lower in the cabinet and then this would give you enough room to actually land the lugs onto the busbars.
It is also considered good trade practice to centre-feed your busbars here to give better current distribution along the busbar.

This sort of wire has a tonne of strands in it and is really flexible.
I'd doubt that this was a factory install, it looks more like something that "happened" on site, no QC guy would ever let an abomination like this leave the factory, if they had any credibility.

The person that did this obviously had no idea what they were doing, irregardless of the fact that (as others have stated above) you have some M8 fuses in there, but you now also have a problem with galvanic corrosion as well, due to the dissimilar metals. frown

Re: No Way!! [Re: Trumpy] #213031
03/08/14 04:40 AM
03/08/14 04:40 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
They could have made this connection just by using longer wires.

I am guessing that white is an ungrounded conductor where you are?
What is neutral?


Greg Fretwell
Re: No Way!! [Re: gfretwell] #213034
03/08/14 07:02 PM
03/08/14 07:02 PM
Trumpy  Offline
OP
Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Originally Posted by gfretwell

I am guessing that white is an ungrounded conductor where you are?
What is neutral?

Greg,
Yes, White is the B phase, it used to be yellow at one time.
Neutral is Black (or light blue if it's in a flexible cord).

Re: No Way!! [Re: Trumpy] #213035
03/08/14 10:32 PM
03/08/14 10:32 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
Quote
Yes, White is the B phase ... Neutral is Black



I guess if you are upside down all the time lots of things are going to be opposite. wink


Greg Fretwell
Re: No Way!! [Re: Trumpy] #213036
03/09/14 10:13 AM
03/09/14 10:13 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Trumpy:

Is that a Siemens breaker??

And, is it common to use color code heat shrink, as opposed to conductors with colored insulation?


John
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,561 Are you busy
180,362 Re: Forum
170,840 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 16 (0.003s) Memory: 1.0252 MB (Peak: 1.2085 MB) Zlib enabled. Server Time: 2018-01-20 09:13:43 UTC