#211822 - 11/17/13 10:22 AM No switched receptacles in patient room?  
brother  Offline
New Member
Joined: Nov 2008
Posts: 7
tn




Can someone help me out here. Had a buddy say AN Inspector says you cannot have switched receptacles in patient rooms. I cannot find it in the NEC or the NFPA 99.

I will admit I can understand the design preference for not doing it but to say it's a code violation is going overboard. BEFORE this guy is challenged on this issue I just wanted to hear from others.


Work Gear for Electricians and the Trades

#211823 - 11/17/13 11:43 AM Re: No switched receptacles in patient room? [Re: brother]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
It is not a fire safety issue...

It's a medical safety issue...

And is almost certainly some sub-set of the building code -- for hospitals.

This is what you must drill into your brain:

Our craft is ruled by a composite of rule books.

The NEC is NOT the end all.

If building a bank... EXTRA rules.

If building a service station... EXTRA rules/ exemptions.

If building a hospital... EXTRA rules... unique to them.

And so it goes.

This is why electrical contractors specialize. Anyone entering these sectors gets BURNED/ blind-sided during their first jobs. They can count themselves lucky to even stay afloat.

BTW, even wiring up elevators is brutal for a 'virgin.'

I had to walk my boss through the procedure. He'd never done one in all his career -- yet he bid the work -- pretty much in the blind. He later admitted he was glad to get out of that job -- with his company intact.

His expertise was in underground/ trunk utilities. Just another area that has EXTRA rules above and beyond the NEC. Once he left that zone -- he was in trouble. He was, however, the king of that domain. It was his bread and butter.



Tesla

#211831 - 11/17/13 02:41 PM Re: No switched receptacles in patient room? [Re: brother]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
You can always ask the inspector what rule he is citing. For any AHJ must be able to back up a statement with a code book and rule.


#211834 - 11/17/13 03:14 PM Re: No switched receptacles in patient room? [Re: brother]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,863
Brick, NJ USA
Harold:
You got it! I would like to hear an NEC Article directly addressing that.

I'm not saying that it could be 'buried' somewhere in 517, but I have not come upon it.



John

#211843 - 11/18/13 12:10 AM Re: No switched receptacles in patient room? [Re: brother]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
But it IS a Code issue: the Building Code -- NOT the NEC.

Can you imagine the confusion/ consequences if someone TURNS OFF a critical receptacle?

There is a LOT of portable electrica apparatus in hospitals these days.

Further, what's the purpose of a switched receptacle in a hospital? I can't imagine any. It's not as if they use floor lamps to light room space -- anywhere.

Just accept the logic and move on.


Tesla

#211845 - 11/18/13 12:44 AM Re: No switched receptacles in patient room? [Re: brother]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,327
Alaska
Still, an inspector should back it up with a reference. Makes things go much smoother. I do it when I wear my inspector hat. It helps me to stay in the book. With all the changes every three years, it's dangerous to shoot from the hip


"Live Awesome!" - Kevin Carosa

#211846 - 11/18/13 02:57 AM Re: No switched receptacles in patient room? [Re: brother]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,113
Estero,Fl,usa
I am guessing California is like Florida. After the electrical inspector/plans examiner looks at the hospital, we have a hospital plan review and inspection by AHCA
http://ahca.myflorida.com/
They have their own rules that go far beyond anything I can enforce via the NEC but it is still on the plan. I can enforce the plan.


Greg Fretwell

#211850 - 11/18/13 04:01 AM Re: No switched receptacles in patient room? [Re: brother]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Without context...

Who's to criticize?

The OP is fuzy on the particulars.

I read it that he's actually shocked that such is so.

As for myself, I would've thought..."could it be any other way?"

Switched receptacles in PATIENT ROOMS -- what's the purpose? Don't tell me he actually had some in mind!

The sole and only classic use for such items was ancient: the need to switch floor lamps. These are now archaic.


Tesla

#211855 - 11/18/13 11:53 AM Re: No switched receptacles in patient room? [Re: brother]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,863
Brick, NJ USA
Most health care facilities here in NJ have Plan Review done by the State (DCA). The DCA approved plans are then forwarded to the respective municipality for fees and issuance of the permits.

Inspections are performed by the municipal inspectors, and upon completion and approvals of the municipal inspections, the State inspections are performed.

And lastly, as I said above, back up the 'violation' with a valid code article.


John

#211856 - 11/18/13 12:05 PM Re: No switched receptacles in patient room? [Re: brother]  
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
The OP is not questioning the fact they should not be switched. He just wants a code reference for it.


Page 1 of 2 1 2

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.023s Queries: 16 (0.004s) Memory: 0.8194 MB (Peak: 1.0016 MB) Zlib enabled. Server Time: 2017-09-21 12:22:33 UTC