ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 3
Recent Posts
Nec circuit protection
by gfretwell. 11/21/17 11:01 PM
FPE in Germany
by Texas_Ranger. 11/19/17 07:30 AM
Ceiling fan distance from outdoor hot tub
by gfretwell. 11/16/17 02:18 AM
diazed fuses
by Texas_Ranger. 11/13/17 03:02 PM
Theft deterrent alarm
by gfretwell. 11/12/17 01:39 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
242,614 Are you busy
178,812 Re: Forum
170,051 Need opinion
Who's Online Now
0 registered members (), 22 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#211708 - 11/12/13 11:58 AM Small transformer better than over sized?  
cgw  Offline
Member
Joined: Jul 2004
Posts: 133
Rochester NY
The load calculated for a (480X208) transformer for multifamily using the optional method (220.84)is significantly smaller than the load calculated using the regular method. It is close but it would allow a smaller transformer (750 vs. 1000).
Are there any disadvantages going with the smaller size?

The advantages are smaller physical size and heat output.


Work Gear for Electricians and the Trades

#211710 - 11/12/13 03:51 PM Re: Small transformer better than over sized? [Re: cgw]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,874
Brick, NJ USA
This is a design issue. Are you refering to the POCO xfr?? Our utility co's here routinely install 'small' transformers (13.2 to 480/13.2 to 120/208) on their supply side.

That said, do you have any capacity for future expansion, if you opt for the smaller unit that you reference as 'close'?

IMHO, a good design would allow for future capacity, unless this resi is being built with no possibility for any significant future electrical requirements. (Such as resi apts)



John

#211720 - 11/12/13 09:59 PM Re: Small transformer better than over sized? [Re: cgw]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
I assumed he was talking about a customer owned transformer.
This may be a Scott question.
At say 600 KVA, is a 1000 KVA more efficient than a 750 (less heat)
I also guess there are higher efficiency transformers for a few extra bucks.
I don't "spec" them I only know how to inspect them wink


Greg Fretwell

#211722 - 11/13/13 09:03 AM Re: Small transformer better than over sized? [Re: cgw]  
ghost307  Offline
Member
Joined: May 2005
Posts: 917
Chicago Illinois USA
The downside that I could see would be if the actual load turned out to be the higher value and you have to go back and replace everything (on your nickel).
If push came to shove, all that the customer's attorney would have to do is point out that the value determined in the Code was indeed greater than the one that you used and claim that you 'cherry picked' another calculation method that let you use the cheapest transformer.

On the other side of the coin, transformers will handle a larger load than they are nameplated at for brief periods of time and you might be okay based on the load profile of the building...but if everyone starts cooking and turns up their thermostats on the same cold winter day you might be up the proverbial creek.


Ghost307

#211725 - 11/13/13 10:48 AM Re: Small transformer better than over sized? [Re: ghost307]  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,223
SI,New Zealand
CGW,
I would never under-spec something like a transformer, especially where it has multiple loads on it, as you state.
You always need a certain amount of operating capacity in a transformer, over and above what your maximum demand calcs tell you, to make sure you don't cause it to overheat or indeed over-saturate.


#211727 - 11/13/13 11:32 AM Re: Small transformer better than over sized? [Re: cgw]  
cgw  Offline
Member
Joined: Jul 2004
Posts: 133
Rochester NY
Thanks for the input.
The question concerns a dry type transformer in the building (the service is 480V and the transformer is for a feeder that serves all the apartments and the 120/208 house loads).
One of the main questions is - do we trust the 220.84 calculation when it is significantly higher than the 220.40 calculation?
Including house load:
220.40 - 945 KVA
220.84 - 664 KVA
750KVA transformer or 1000KVA transformer?


#211728 - 11/13/13 03:40 PM Re: Small transformer better than over sized? [Re: cgw]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,874
Brick, NJ USA
IMHO, 220.40 would be my choice.

1000KVA transformer.

(Keep in mind that it will all come back to the design professional, in the event of any issues)

Last edited by HotLine1; 11/13/13 03:43 PM.

John

#211729 - 11/13/13 03:43 PM Re: Small transformer better than over sized? [Re: cgw]  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Several years ago the US government passed an 'Energy Act'. One of the most visible outcomes was the 'killing off' of incandescent lamps, another was the requirement that small power transformers (e.g. non-utility installations) be designed with 'ideal' efficiency at 35% loading.

So a 1000kVA transformer would be most efficient at 350kVA, but it may still be less efficient than a 350kVA unit loaded to 100%.

Have you done a loss (cost of ownership) analysis yet?






#211740 - 11/14/13 01:49 AM Re: Small transformer better than over sized? [Re: cgw]  
twh  Offline
Member
Joined: Mar 2004
Posts: 922
Regina, Sask.
Smaller transformers require smaller wire and possibly equipment.


#211801 - 11/16/13 04:43 PM Re: Small transformer better than over sized? [Re: cgw]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
The step-wise introduction of LEDs and less consumptive PCs...now replaced by laptops... means that you would go small.

You're burning kW even at idle. The rare heavy loads can be sustained for hours on end for such transformers.

Be certain that ventilation is good and pure. If it is not so then you have to go large.

You would not believe how hot some e-rooms get because the design disregarded heat-rejection from a dry-type transformer.


Last edited by Tesla; 11/16/13 04:44 PM.

Tesla

Page 1 of 2 1 2

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.024s Queries: 16 (0.003s) Memory: 0.8203 MB (Peak: 1.0076 MB) Zlib enabled. Server Time: 2017-11-22 12:41:29 UTC