#211364 - 10/08/13 03:19 PM GFCI receptacle used as a disconnect?  
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
Can a GFCI receptacle be used as a disconnecting means for an out building (fed by only a single circuit) using the test button? I say no, but I saw this done over the weekend at a friend's place and he swears that it was inspected. I don't believe him.


---Ed---

"But the guy at Home Depot said it would work."

2017 / 2014 NEC & Related Books and Study Guides

#211366 - 10/08/13 03:32 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,824
Brick, NJ USA
IMHO, No!


John

#211372 - 10/08/13 10:20 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]  
NickD  Offline
Member
Joined: Mar 2013
Posts: 46
Amish Country, PA
A GFCI CAN be used as a disconnecting means... that is what is supposed to do. This is not up for debate. Whether or not it is acceptable practice is the question.

A little more detail would be helpful, otherwise we'll be answering your question on a lot of assumptions.
There is a circuit, starting with a GFCI at the main building, which then runs to the out building?
Depending on the specific situation and the wiring in the outbuilding (the fact that it is only one circuit), I could see it being passed by an AHJ.

Last edited by NickD; 10/08/13 10:23 PM.

#211377 - 10/08/13 10:30 PM Re: GFCI receptacle used as a disconnect? [Re: NickD]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,322
Alaska
GFCI's are not listed as a service disconnect thus can not be used as one


"Live Awesome!" - Kevin Carosa

#211378 - 10/08/13 10:52 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
The only exception to 225.38 is that a snap switch can be used in garages and out buildings on residential properties.
Nothing about a GFCI


Greg Fretwell

#211379 - 10/08/13 10:54 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,824
Brick, NJ USA
Again & IMHO no it cannot be a disconnect. Yes, in theory pushing the 'test' button will open the circuit, but it is not manufactured, designed or intended as a disconnect.


John

#211380 - 10/08/13 10:58 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
Sorry 225.36


Greg Fretwell

#211382 - 10/08/13 11:04 PM Re: GFCI receptacle used as a disconnect? [Re: EV607797]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,824
Brick, NJ USA
Greg:
225.36 from 2011:
225.36 Suitable for Service Equipment. The disconnecting
means specified in 225.31 shall be suitable for use as
service equipment.
Exception: For garages and outbuildings on residential
property, a snap switch or a set of 3-way or 4-way snap
switches shall be permitted as the disconnecting means.

You are agreeing that a GFI cannot be used??


John

#211387 - 10/09/13 01:02 AM Re: GFCI receptacle used as a disconnect? [Re: EV607797]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,076
Estero,Fl,usa
Yes. It is not a snap switch and it is not suitable as service equipment as AK sparky pointed out.


Greg Fretwell

#211388 - 10/09/13 02:09 AM Re: GFCI receptacle used as a disconnect? [Re: gfretwell]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,322
Alaska
Test buttons don't always work on them


"Live Awesome!" - Kevin Carosa

Page 1 of 2 1 2

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 16 (0.004s) Memory: 0.8193 MB (Peak: 0.9993 MB) Zlib enabled. Server Time: 2017-05-24 04:08:51 UTC