#211034 - 09/06/13 09:51 PM RV park remote meter centers need main disconnect?  
bigpapa  Offline
Member
Joined: Mar 2006
Posts: 81
canada
I am looking for opinions on this RV park install, or possibly some code rules that are less obvious.


First we will install a main service with breakers and feeders for several meter stacks. The meter stacks will then feed a bunch new 50A 120/240V RV pedestals. Each pedestal will have its own meter and breaker in the stack.


The arrangement is pretty much the same as you would see in a typical residential high rise where there are usually no main disconnects in the meter closets.

The difference is that since our meter closet kiosks are distributed outdoors throughout the park they are technically different buildings. I am leaning towards including the disconnects because of this.

I talked to the inspector but he wouldn't comment on design issues.
They don't really have time for this when I call at 3:30 on a Friday I gather.

If anyone cares to comment please do.


Tools for Electricians:

#211042 - 09/08/13 04:27 PM Re: RV park remote meter centers need main disconnect? [Re: bigpapa]  
twh  Offline
Member
Joined: Mar 2004
Posts: 915
Regina, Sask.
72-104 allows USEI and you could treat each distribution centre as a service. It would be tempting to do this because of the issue of different potentials between ground and neutral over distances (and cable cost). If you ran ACWU with a separate ground, I'm not aware of any rule requiring a disconnect at each building where it isn't a service.

Perhaps the inspector wouldn't comment on design issues because the inspectors don't agree on whether a main disconnect is required on a sub-panel where the sub panel is in a separate building and this is similar.

Be aware that entrance switches can't be in public areas unless "adequate precautions are taken to prevent interference", under 9.26.1.3 of the National Building Code of Canada.


#211049 - 09/08/13 10:39 PM Re: RV park remote meter centers need main disconnect? [Re: twh]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,321
Alaska
There's no breakers in the pedistals?


"Live Awesome!" - Kevin Carosa


Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,707
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.003s) Memory: 0.7524 MB (Peak: 0.8784 MB) Zlib enabled. Server Time: 2017-05-24 00:26:06 UTC