Underground Conduit Handholes #210912
08/21/13 01:47 PM
08/21/13 01:47 PM
C
cgw  Offline OP
Member
Joined: Jul 2004
Posts: 133
Rochester NY
If we install a underground conduit (say 3") between buildings (say 600 feet-ish or more) for fiber. For straight runs how far should handholes be spaced for pulling?

Work Gear for Electricians and the Trades
Re: Underground Conduit Handholes [Re: cgw] #210913
08/21/13 07:09 PM
08/21/13 07:09 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,917
Brick, NJ USA
A few considerations:
Fiber mfg specs for pull tension?
Pulling equipment limitations?
Pull rope length?

600' straight may be 'one shot' pull.



John
Re: Underground Conduit Handholes [Re: cgw] #210942
08/27/13 11:23 AM
08/27/13 11:23 AM
S
sabrown  Offline
Member
Joined: Dec 2002
Posts: 302
Ogden, Utah, USA
EIA/TIA documents and specificaions likely have something to say about this. Other things to consider:

How many different cables with fiber?

Are they in innerduct? Pulling innerduct would limit distances. Some pre-terminated cables come in innerduct as part of the assembly.

Are they gopher rated cables being pulled in? Gopher rated means shielding against burrowing critters. Makes them harder to pull, but may increase allowed pulling tensions.

Is conduit sizing based on future pulls possible/likely?
Do the specs, manufacturer, or EIA/TIA allow soap? Soap is another name for a lubricant that eases pulling of cable.

For pulling refer also to BICSI ITSIM, Ch. 4, "Pulling Cable."

I am sorry that my memory is not as good as it used to be, years ago I helped with some revisions to the EIA/TIA documents, but I have forgotten more than I have ever learned.

Shnae

Re: Underground Conduit Handholes [Re: cgw] #210943
08/27/13 11:23 AM
08/27/13 11:23 AM
S
sabrown  Offline
Member
Joined: Dec 2002
Posts: 302
Ogden, Utah, USA
I can't even remember how to spell my name.

Shane


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,547 Are you busy
180,358 Re: Forum
170,836 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.9580 MB (Peak: 1.0913 MB) Zlib enabled. Server Time: 2018-01-19 15:36:03 UTC