NEC Article 490 #210209
06/03/13 01:39 PM
06/03/13 01:39 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
Hi,
Is it a requirement that raceways entering metal enclosed switchgear over 600 VAC be in rigid conduit or can I come from a transformer to a 4160 switch with duct bank comprised of PVC and bell end reducers?

Here is an article on this:
http://books.google.com/books?id=h2...ge&q=NEC%20Article%20490&f=false

Thanks

Greg


Don't drive and TEXT! Drive now TALK LATER!
2017 / 2014 NEC & Related Books and Study Guides
Re: NEC Article 490 [Re: akmaster] #210218
06/03/13 06:55 PM
06/03/13 06:55 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
I don't know of anything about metal enclosures and plastic raceways other than the need for a hard wired EGC connected to a dedicated terminal in the enclosure.

OTOH going the other way (metal raceway, plastic box) is a tougher sell. You need a positive way of bonding the raceway.


Greg Fretwell
Re: NEC Article 490 [Re: akmaster] #210226
06/04/13 12:32 PM
06/04/13 12:32 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
Thanks Greg, I will go take some pics and post them..Seems I read something in OSHA about metal clad switchgear over 600V had to be in RGS...we have a 115kV transformer stepped down to 13.8 kV...the risers and duct bank for the secondary to the metal clad switch gear is schedule 80 PVC..

The risers from the switchgear feeding out to the various transformers and electrical control rooms are pvc with RGS elbows and pvc risers...this is 13.8 and 4.16 kV..

Was thinking OSHA had requirements for circuits over 600VAC requiring steel conduit entering the metal clad gear..

Thank you,

Greg


Don't drive and TEXT! Drive now TALK LATER!
Re: NEC Article 490 [Re: akmaster] #210227
06/04/13 12:40 PM
06/04/13 12:40 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
That may be true. The NEC is just one piece of the puzzle.



Greg Fretwell
Re: NEC Article 490 [Re: akmaster] #210228
06/04/13 12:42 PM
06/04/13 12:42 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
Does the 2005 code requre the 18" depth for RGS elbows or has that changed since then? I do not have a 2005 NEC code book..

so if anyone knows if it is the same requirement now as it was then please let me know.

thanks

Greg


Don't drive and TEXT! Drive now TALK LATER!
Re: NEC Article 490 [Re: akmaster] #210234
06/04/13 02:45 PM
06/04/13 02:45 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,917
Brick, NJ USA
IF the entire sweep is 18" under ground, there is no need to bond that metalic raceway. However, run a metalic riser above grade, and it must be bonded.

This has been the way it is for a longer time than I would care to admit.

BTW, all the MV jobs I have been around are in RGS above ground. 4160, 13.2, etc.




John
Re: NEC Article 490 [Re: akmaster] #210237
06/04/13 02:52 PM
06/04/13 02:52 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
thank you hotline...

greg


Don't drive and TEXT! Drive now TALK LATER!

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 20
Potseal 13
Popular Topics(Views)
243,539 Are you busy
180,341 Re: Forum
170,831 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.008s) Memory: 0.9849 MB (Peak: 1.1409 MB) Zlib enabled. Server Time: 2018-01-18 21:41:33 UTC