ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 5
Recent Posts
What do you do?
by HotLine1. 09/20/17 08:44 PM
Supporting conduit bodies
by ghost307. 09/18/17 12:12 PM
Thermal Imaging Camera upgrade
by Potseal. 09/18/17 11:57 AM
Linear Power Supply Quits Under Load
by JoeTestingEngr. 09/15/17 11:37 PM
Recreational Trailer Power Supply
by David1. 09/14/17 01:55 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,843 Are you busy
176,602 Re: Forum
168,518 Need opinion
Who's Online Now
0 registered members (), 50 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#210167 - 05/31/13 10:14 AM Transformer rating  
cgw  Offline
Member
Joined: Jul 2004
Posts: 133
Rochester NY
1. When the NEC refers to a Class 155 transfomer is that the same as a manufacturer's temeperature rise?

2. When the NEC requires that the transformer be installed in a transformer room does that mean a separate room from the electric switchgear and other mechanicals?


2017 / 2014 NEC & Related Books and Study Guides

#210169 - 05/31/13 05:23 PM Re: Transformer rating [Re: cgw]  
ghost307  Offline
Member
Joined: May 2005
Posts: 910
Chicago Illinois USA
1. No. The temperature rise is stated as the maximum temperature rise above the room ambient. I think what you are referring to as 'Class 155' is a rating of the temperature at which the insulation system fails and the transformer becomes a giant flash bulb.
2. Yes and No. It needs to be in a room separate from things that are not directly associated with the electrical system. That means no chillers, fans, pumps, phone equipment, etc.


Ghost307

#210194 - 06/02/13 06:32 PM Re: Transformer rating [Re: cgw]  
cgw  Offline
Member
Joined: Jul 2004
Posts: 133
Rochester NY
Thanks
(I figured 1. out right after I posted)
Is your typical low voltage (say 480X208/120) dry type transformer considered totally enclosed except for the ventilating openings?


#210201 - 06/02/13 10:17 PM Re: Transformer rating [Re: cgw]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,863
Brick, NJ USA
The term 'totally enclosed' does not specifically appear in Art. 100 or 450 (2011 NEC)

Mention is made within 450.21
"450.21 Dry-Type Transformers Installed Indoors.
(A) Not over 1121⁄2 kVA. Dry-type transformers installed
indoors and rated 1121⁄2 kVA or less shall have a separation
of at least 300 mm (12 in.) from combustible material unless
separated from the combustible material by a fireresistant,
heat-insulated barrier.
Exception: This rule shall not apply to transformers rated
for 600 volts, nominal, or less that are completely enclosed, with or without ventilating openings.
(B) Over 1121⁄2 kVA. Individual dry-type transformers of
more than 1121⁄2 kVA rating shall be installed in a transformer room of fire-resistant construction. Unless specified otherwise in this article, the term fire resistant means a construction having a minimum fire rating of 1 hour.
Exception No. 1: Transformers with Class 155 or higher
insulation systems and separated from combustible material
by a fire-resistant, heat-insulating barrier or by not less
than 1.83 m (6 ft) horizontally and 3.7 m (12 ft) vertically.
Exception No. 2: Transformers with Class 155 or higher
insulation systems and completely enclosed except for ventilating openings."

IMHO, a basic 480/120-208 transformer is 'enclosed' by def.; and 'completely' enclosed as the wording within exception 2 above.

A 'totally enclosed' transformer IMHO, is one that is encapsulated and only the pri & sec conductors are visable.


John


Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.004s) Memory: 0.7612 MB (Peak: 0.8927 MB) Zlib enabled. Server Time: 2017-09-21 13:56:12 UTC