Manholes #210161
05/30/13 04:40 PM
05/30/13 04:40 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
Is there a article in the code that requires a slope of 3% oriented to the manhole? Or does it cover that at all?

Please quote article if possible.

Thank you.

Greg


Don't drive and TEXT! Drive now TALK LATER!
2017 / 2014 NEC & Related Books and Study Guides
Re: Manholes [Re: akmaster] #210163
05/30/13 04:58 PM
05/30/13 04:58 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
I believe article 310 covers manholes..


Don't drive and TEXT! Drive now TALK LATER!
Re: Manholes [Re: akmaster] #210173
05/31/13 07:03 PM
05/31/13 07:03 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Is the manhole owned by a utility company or privately owned? Is this a service wire, feeder wire from 1 building to another? Maybe the guys need a little more info.

Re: Manholes [Re: akmaster] #210175
05/31/13 07:20 PM
05/31/13 07:20 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
It is one of many manholes on an ethanol project...it will contain Medium voltage cables (4160) fiber and control and DC circuits..the are 8'x 8'x8'. They have a base and a top...
the specs call for a 0.3% slope TOWARDS the manhole..

I did not find that requirement anywhere in the code..

It seems they will need racks inside to rack the cables as well..

Thanks,
Greg


Don't drive and TEXT! Drive now TALK LATER!
Re: Manholes [Re: akmaster] #210176
05/31/13 08:24 PM
05/31/13 08:24 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
Toward the manhole? Is this also the storm drain system?


Greg Fretwell
Re: Manholes [Re: akmaster] #210182
06/01/13 01:36 PM
06/01/13 01:36 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,


Check sec. 110 V of the NEC, that talks about manholes and their construction also sec. 490 talks about voltage over 600. You also might have to refer to the National Safety Code. Most utilities follow those rules. I might have an old NESC book around, I would have to look.

Re: Manholes [Re: akmaster] #210186
06/01/13 03:39 PM
06/01/13 03:39 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
This may say something: From '08 Handbook:

"110.70 General.
Electrical enclosures intended for personnel entry and specifically fabricated for this purpose shall be of sufficient size to provide safe work space about electrical equipment with live parts that is likely to require examination, adjustment, servicing, or maintenance while energized. Such enclosures shall have sufficient size to permit ready installation or withdrawal of the conductors employed without damage to the conductors or to their insulation. They shall comply with the provisions of this part.
Exception: Where electrical enclosures covered by Part V of this article are part of an industrial wiring system operating under conditions of maintenance and supervision that ensure that only qualified persons monitor and supervise the system, they shall be permitted to be designed and installed in accordance with appropriate engineering practice. If required by the authority having jurisdiction, design" (documentation may be required)

Last edited by HotLine1; 06/01/13 03:41 PM. Reason: added text in parenthesis

John
Re: Manholes [Re: akmaster] #210208
06/03/13 01:17 PM
06/03/13 01:17 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
Thanks for the replies. @ Greg...yes towards the manhole...

@hotline...thanks I will take a look...

I can not find any requirement regarding slope of 0.3 percent towards the manhole for conduits...

does this include the whole run from man hole to man hole?

regards

Greg


Don't drive and TEXT! Drive now TALK LATER!
Re: Manholes [Re: akmaster] #210230
06/04/13 01:15 PM
06/04/13 01:15 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
Another question: Is it not a requirement that manholes with high voltage are required to have the cover labeled "DANGER HIGH VOLTAGE"?

Thanks

GW

Last edited by akmaster; 06/04/13 01:15 PM.

Don't drive and TEXT! Drive now TALK LATER!
Re: Manholes [Re: akmaster] #210231
06/04/13 01:25 PM
06/04/13 01:25 PM
akmaster  Offline OP
Member
Joined: Jun 2012
Posts: 70
alaska
One more...Does the Manhole cover have to be grounded?


Don't drive and TEXT! Drive now TALK LATER!
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,522 Are you busy
180,321 Re: Forum
170,812 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 16 (0.003s) Memory: 1.0252 MB (Peak: 1.2078 MB) Zlib enabled. Server Time: 2018-01-17 15:04:33 UTC