#208851 - 02/15/13 11:21 AM Wet loc or damp loc?  
BigB  Offline
Member
Joined: Mar 2004
Posts: 719
Tucson, AZ USA
Is a shower ceiling considered a wet location or a damp location? Would a fan/fixture located in a shower ceiling have to show the rating in addition to stating that it is suitable for installation above a shower (along with GFCI requirements of course)?


2017 / 2014 NEC & Related Books and Study Guides

#208852 - 02/15/13 01:24 PM Re: Wet loc or damp loc? [Re: BigB]  
LEO_304E  Offline
Member
Joined: Oct 2010
Posts: 17
MASSACHUSETTS
Originally Posted by BigB
Is a shower ceiling considered a wet location or a damp location? Would a fan/fixture located in a shower ceiling have to show the rating in addition to stating that it is suitable for installation above a shower (along with GFCI requirements of course)?
Yes ,It is a wet location.

I believe that all the fixtures rated for a shower area are also marked wet location.


#208853 - 02/15/13 01:34 PM Re: Wet loc or damp loc? [Re: BigB]  
LEO_304E  Offline
Member
Joined: Oct 2010
Posts: 17
MASSACHUSETTS
Originally Posted by BigB
Is a shower ceiling considered a wet location or a damp location? Would a fan/fixture located in a shower ceiling have to show the rating in addition to stating that it is suitable for installation above a shower (along with GFCI requirements of course)?


Here is the 2011 NEC.

410.10 (D) Bathtub and Shower Areas. No parts of cord-connected
luminaires, chain-, cable-, or cord-suspended luminaires, lighting
track, pendants, or ceiling-suspended (paddle) fans shall
be located within a zone measured 900 mm (3 ft) horizontally
and 2.5 m (8 ft) vertically from the top of the bathtub rim or
shower stall threshold. This zone is all encompassing and includes
the space directly over the tub or shower stall. Luminaires
located within the actual outside dimension of the bathtub
or shower to a height of 2.5 m (8 ft) vertically from the top
of the bathtub rim or shower threshold shall be marked for
damp locations, or marked for wet locations where subject to
shower spray.



So the fixtures must be marked at least damp locations.


#208855 - 02/15/13 03:13 PM Re: Wet loc or damp loc? [Re: BigB]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
I am not sure where it says GFCI is required.

The handbook says "GFCI protection is required only where specified in the installation instructions for the luminaire."


Greg Fretwell

#208862 - 02/16/13 01:27 PM Re: Wet loc or damp loc? [Re: BigB]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Not unless the manufacture is requiring it? However if you have a very high ceiling above a shower stall, say 15 feet high, would that still be wet location? How about damp location?


#208865 - 02/16/13 02:24 PM Re: Wet loc or damp loc? [Re: BigB]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Harold:
"Luminaires located within the actual outside dimension of the bathtub or shower to a height of 2.5 m (8 ft) vertically from the top of the bathtub rim or shower threshold shall be marked for damp locations, or marked for wet locations where subject to shower spray."

To a height of 8' takes care of the tall ceilings. However, IF there is a chance the shower could spray up, then...all bets are off, and it's wet.



John

#208877 - 02/17/13 12:50 PM Re: Wet loc or damp loc? [Re: gfretwell]  
Theelectrikid  Offline
Member
Joined: Apr 2004
Posts: 810
Levittown, PA
Originally Posted by gfretwell
I am not sure where it says GFCI is required.

The handbook says "GFCI protection is required only where specified in the installation instructions for the luminaire."


I know bath fans are typically rated for use right in the shower if they're downstream of a GFCI. Haven't seen a fixture for that otherwise since we usually do a hi-hat and shower trim.


Is there anyone on board who knows how to fly a plane?

#208891 - 02/19/13 12:44 AM Re: Wet loc or damp loc? [Re: BigB]  
BigB  Offline
Member
Joined: Mar 2004
Posts: 719
Tucson, AZ USA
Yes I did mean GFCI by manufacturer requirements. Seems the "wet location if subject to shower spray" is a judgement call open for arguement, however it may be a moot point anyway as Leo said the fixtures rated for shower/tub area are all wet location fixtures anyway, and at least all the ones I could find were.


#208949 - 02/23/13 02:25 PM Re: Wet loc or damp loc? [Re: BigB]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
John,

OK I agree if there is a chance of spray, then the light should be listed for a damp/wet location. However if you have a ceiling that is say, 15 feet above the shower, it is highly unlikely that if would be subject to water spray. Unless you let little kids with a bad snense of humor using a handheld shower head on "Stream" and shooting it straight in the air. Then in that case, the sink lights might also be subject to wet location, depending on the power of the handheld sprayer. smile



Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.026s Queries: 15 (0.004s) Memory: 0.8034 MB (Peak: 0.9769 MB) Zlib enabled. Server Time: 2017-10-19 16:05:42 UTC