#206953 - 09/07/12 09:48 AM Underground Feeders to fire pump  
beatricellc  Offline
New Member
Joined: Jul 2012
Posts: 6
cook county, IL
In a Chicago high rise, feeders to a fire pump are below the floor of a parking garage. Fire pump controller is from around 1959. 480V 3 phase/ 150hp.

About 250' from the meter, there is a junction box in the floor. It is about another 100' to the fire pump. There is 3" conduit, and fiber bushings, at opposite ends of the rectangle shaped box. The box is falling apart. The conduit end, at the fire pump side of the box, is collapsing and closing in on the wire. There are 3 feeders. The insulation from one of the feeders is not cut but is "bulging" from the squeeze.

If after I megger the wire and find it to be OK. Can I just repair the damaged feeder? Is it acceptable to "sleeve" the damaged conduit end with an insulator?


2017 / 2014 NEC & Related Books and Study Guides

#206954 - 09/07/12 10:24 AM Re: Underground Feeders to fire pump [Re: beatricellc]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,853
Brick, NJ USA

That answer is best for you IF it comes from the local AHJs.


John

#206955 - 09/07/12 12:35 PM Re: Underground Feeders to fire pump [Re: beatricellc]  
beatricellc  Offline
New Member
Joined: Jul 2012
Posts: 6
cook county, IL
What is an AHJ?


#206956 - 09/07/12 12:48 PM Re: Underground Feeders to fire pump [Re: beatricellc]  
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
Authority Having Jurisdiction. Inspectors.


#206957 - 09/07/12 02:08 PM Re: Underground Feeders to fire pump [Re: beatricellc]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
I agree with John. Get your local electrical inspector in there, show him the problem and see what you can work out.

From the sound of it, you might be chipping up some floor. These days with diamond saws and air tools, it is usually not that big a deal. You might be meeting a guy from the concrete worker's union tho (in Chicago).

Once you get it opened up you should be able to get back to clean pipe and extend it a little, into your new enclosure or just use a bigger box.


Greg Fretwell

#206958 - 09/07/12 06:54 PM Re: Underground Feeders to fire pump [Re: beatricellc]  
beatricellc  Offline
New Member
Joined: Jul 2012
Posts: 6
cook county, IL
Thanks. I was looking into cutting the floor and a new box as the next option.


#206959 - 09/07/12 08:34 PM Re: Underground Feeders to fire pump [Re: beatricellc]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,853
Brick, NJ USA
The point of where I was going with a suggestion is that you should have a talk with the electrical inspector, and possibly the fire inspector before you plan any repairs.

Discussion regarding what is acceptable, and providing details (sketch) is a lot easier than doing something & not having it approved.


John


Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.7852 MB (Peak: 0.9423 MB) Zlib enabled. Server Time: 2017-07-24 10:46:05 UTC