ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
MRI LED lights dimmer control replacement - wow!
by Potseal. 01/19/18 08:52 PM
VDE 0100 to introduce AFCIs
by sparky. 01/19/18 08:03 PM
Video: Inventor of the GFCI self-testing shocks
by Bill Addiss. 01/17/18 11:11 PM
FPE in Germany
by HotLine1. 01/17/18 07:07 PM
Fujifilm Recalls Power Adapter Wall Plugs
by Admin. 01/16/18 07:04 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 14 guests, and 12 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
type NM in conduit #206304
06/15/12 10:27 AM
06/15/12 10:27 AM
J
jkraft  Offline OP
Member
Joined: May 2003
Posts: 74
Hello,
Can someone direct me to the NEC section regarding sleeveing romex in conduit for a combination of 12/2 and 14/2, over 10'
thanks,
Joe

2017 / 2014 NEC & Related Books and Study Guides
Re: type NM in conduit [Re: jkraft] #206307
06/15/12 11:14 AM
06/15/12 11:14 AM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
334.15(B)
Quote
Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means extending at least 150 mm (6 in.) above the floor.


Note 9 to table 9 (conduit fill) says
Quote
(9)A multiconductor cable or flexible cord of two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. For cables that have elliptical cross sections, the cross-sectional area calculation shall be based on using the major diameter of the ellipse as a circle diameter.


two cables can't be stacked and measured, You have to compute for "2 conductors" the size of the widest dimension so you end up with some pretty big pipe.
I haven't run the numbers on a 12 and a 14 but 1" would not surprise me


Greg Fretwell
Re: type NM in conduit [Re: gfretwell] #206308
06/15/12 11:41 AM
06/15/12 11:41 AM
J
jkraft  Offline OP
Member
Joined: May 2003
Posts: 74
thanks for your help Greg, looking at those sections now and trying to determine what size IMC would be needed for 1-12/2 and 2-14/2???

Re: type NM in conduit [Re: jkraft] #206309
06/15/12 01:03 PM
06/15/12 01:03 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
OK lets run the numbers
I will use commie metric because I prefer decimals

The 14ga I have measures 9mm, 12ga measures 10mm (across the widest part.

The area is the radius (half the diameter above)squared times pi (3.14)

5 x 5 x 3.14 = 78.5 mm2
4.5 x 4.5 x 3.14 = 63.6 mm2
Total cable area = 142.1 mm2

Take that to table 9 IMC "2 wire" column and you end up with 1" IMC (up to 192 mm2)
3/4 only gives you 117 mm2

See why I wasn't surprised? wink



Greg Fretwell
Re: type NM in conduit [Re: jkraft] #206316
06/15/12 08:59 PM
06/15/12 08:59 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Nice answer Greg. Not everyone knows about this approach. Most contractors want to skin the outer jacket from the NM cable and not worry about the rules. A clear violation of 312.5(C)(e).

Last edited by George Little; 06/15/12 09:12 PM.

George Little
Re: type NM in conduit [Re: jkraft] #206317
06/15/12 10:27 PM
06/15/12 10:27 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Greg:
Ditto with what George said! Nice!!


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,560 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.9761 MB (Peak: 1.1252 MB) Zlib enabled. Server Time: 2018-01-20 05:17:33 UTC