afci/gfci protection for 2 wire recepts. #206148
05/29/12 06:26 PM
05/29/12 06:26 PM
C
crselectric  Offline OP
Member
Joined: Sep 2006
Posts: 133
albany, ca
I'm doing a service change at a Cal. house that has had all its 2 wire K&T recept.s swapped for ungrounded 3wire recept....Will a combo Afci/Gfci bkr meet with no equipment ground label. or do I have to put gfci prot label as well, HO is trying to sell house, or do I talk him into replacing with non-ground TR's 2010 CEC, thanks Chris I have not done any rewiring ex. refeed the closet fuse box to splices only. C

2017 / 2014 NEC & Related Books and Study Guides
Re: afci/gfci protection for 2 wire recepts. [Re: crselectric] #206164
05/30/12 08:22 PM
05/30/12 08:22 PM
C
crselectric  Offline OP
Member
Joined: Sep 2006
Posts: 133
albany, ca
My question is will a combo afci/gfci breaker meet the gfci req. for replaced receptacles on K&T circuits, also has anyone seen tamper resist. 2-wire recept.s

Re: afci/gfci protection for 2 wire recepts. [Re: crselectric] #206165
05/30/12 08:37 PM
05/30/12 08:37 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,917
Brick, NJ USA
I have not seen any TR two wire receptacles, and none are in the P&S literature I have.

I have to ask....why TR?? Is that a CEC thing?


John
Re: afci/gfci protection for 2 wire recepts. [Re: crselectric] #206166
05/30/12 08:40 PM
05/30/12 08:40 PM
C
crselectric  Offline OP
Member
Joined: Sep 2006
Posts: 133
albany, ca
My question is will a combo afci/gfci breaker meet the gfci req. for replaced receptacles on K&T circuits, also has anyone seen tamper resist. 2-wire recept.s

Re: afci/gfci protection for 2 wire recepts. [Re: crselectric] #206167
05/30/12 08:46 PM
05/30/12 08:46 PM
C
crselectric  Offline OP
Member
Joined: Sep 2006
Posts: 133
albany, ca
Oh the Inspector has stated on a corr. notice that recept.s be two-wire of TR type, for all replaced knob and tube outlets. The Homeowner bought the place with the plugs already replaced, I guess it passed the selling inspection 13 years ago when he bought it. He's now trying to make the service safer instead of being in a cabinet at grade with the gas meter, opened a can of worms

Re: afci/gfci protection for 2 wire recepts. [Re: crselectric] #206168
05/30/12 08:50 PM
05/30/12 08:50 PM
C
crselectric  Offline OP
Member
Joined: Sep 2006
Posts: 133
albany, ca
or gfci protected and labeled no eq. ground, gfci prot.,

Re: afci/gfci protection for 2 wire recepts. [Re: crselectric] #206172
05/31/12 01:20 AM
05/31/12 01:20 AM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
I think a GFCI breaker would allow replacement with the TR 5-15s.
406.3(D)(3)(c) in 2008 406.3(D)(2)(c) in 2011

Quote
(c) A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked “GFCI Protected” and “No Equipment Ground.” An equipment grounding conductor shall not be connected between the grounding-type receptacles.



The requirement for AFCI would be a local call. A breaker incorporating both should work

The 2011 code requires this effective 1/1/14
406.3(D)(4)


Greg Fretwell
Re: afci/gfci protection for 2 wire recepts. [Re: crselectric] #206173
05/31/12 02:07 AM
05/31/12 02:07 AM
C
crselectric  Offline OP
Member
Joined: Sep 2006
Posts: 133
albany, ca
thanks greg, I do believe he was stating the 2008 code for TR recept.s but also didnt write a correction but said all convenience receptacles should be afci protected. but that was for new circuits, and all I've run are circuits to refeed the old fuse panel,

Re: afci/gfci protection for 2 wire recepts. [Re: crselectric] #206174
05/31/12 02:27 AM
05/31/12 02:27 AM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
AFCI on old work seems to be all over the place depending on how your "rehab/existing building" codes are written and what your AHJ wants. I usually avoid trying to guess what the local guys want. If the 2011 is adopted and they leave 406.3 intact a lot of that indecision will go away. You will be doing AFCI and GFCI on any replacements after 1/1/14 the way I read it.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 20
Potseal 13
Popular Topics(Views)
243,539 Are you busy
180,341 Re: Forum
170,831 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.003s) Memory: 1.0012 MB (Peak: 1.1714 MB) Zlib enabled. Server Time: 2018-01-18 23:41:39 UTC