Interesting spin on 430.22(B) #205918
04/25/12 01:31 PM
04/25/12 01:31 PM
G
gfretwell  Online Content
OP
Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
If a guy used 430.52 to size his breaker and ended up with a hard wired pool pump on a single pole 30, he would not need GFCI.

Quote
(B) GFCI Protection. Outlets supplying pool pump motors from branch circuits with short-circuit and ground-fault protection rated 15 or 20 amperes, 125 volt or 240 volt, single phase, whether by receptacle or direct connection, shall be provided with ground-fault circuit-interrupter protection for personnel.


Greg Fretwell
2017 / 2014 NEC & Related Books and Study Guides
Re: Interesting spin on 430.22(B) [Re: gfretwell] #205919
04/25/12 06:43 PM
04/25/12 06:43 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,919
Brick, NJ USA
Greg:
Yes, that scenario would fly. I have not seen anyone go down that path, & I would not be the guide.

Yes, as you say, it would be compliant, and acceptable using that path, but...if I was the EC, I would not go there. GFI protection costs are not that high.

Let's see what everybody else says!!


John
Re: Interesting spin on 430.22(B) [Re: gfretwell] #205921
04/26/12 02:25 PM
04/26/12 02:25 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
What's the surprise? Heck, use a 10-amp breaker and it works too!

Put your house on 10-amp breakers and you don't need AFCI's laugh ..... as a result of the NEC using the exact sort of language.

Re: Interesting spin on 430.22(B) [Re: gfretwell] #205930
04/27/12 09:12 PM
04/27/12 09:12 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
The problem I can see with house on 10 Amp circuits not needing AFCI?...... There aren't any 10 Amp receptacles. smile

Re: Interesting spin on 430.22(B) [Re: gfretwell] #205935
04/29/12 01:21 AM
04/29/12 01:21 AM
G
gfretwell  Online Content
OP
Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
This actually came up on a home owner BB. The guy had a pool pump on a 25 (2 pole).

I suggested the right fix was a 20A GFCI but the code question did nag me.
I do believe, if your pool pump is tripping a GFCI, you have a bad pool pump.


Greg Fretwell
Re: Interesting spin on 430.22(B) [Re: gfretwell] #205936
04/29/12 01:28 AM
04/29/12 01:28 AM
G
gfretwell  Online Content
OP
Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
I have heard a couple of discussions about the 10a breaker thing.
The first issue is the number of 10a circuits you would need to get the 3va per sq foot. That might be a show stopper right there.
The other one is the 210.21(B)(2) problem.

I have heard a more compelling argument if the 10a only served the smoke alarms. That could make some sense.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,597 Are you busy
180,402 Re: Forum
170,868 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.9770 MB (Peak: 1.1268 MB) Zlib enabled. Server Time: 2018-01-23 06:09:17 UTC