ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 5
Recent Posts
What do you do?
by gfretwell. 09/18/17 08:17 PM
Supporting conduit bodies
by ghost307. 09/18/17 12:12 PM
Thermal Imaging Camera upgrade
by Potseal. 09/18/17 11:57 AM
Linear Power Supply Quits Under Load
by JoeTestingEngr. 09/15/17 11:37 PM
Recreational Trailer Power Supply
by David1. 09/14/17 01:55 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,825 Are you busy
176,586 Re: Forum
168,507 Need opinion
Who's Online Now
0 registered members (), 36 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#205568 - 03/09/12 05:18 PM mca and mocp nameplate  
Bravo  Offline
Member
Joined: May 2010
Posts: 30
NY, USA
Hi have a chiller rated 208V, 3P, MCA: 46.1, MOPD: 80, RLA: 30. Its been awhile for sizing motor branch ckts but any idea how to size the ckt. & OCPD?

Correct me if I am wrong but last I remember based on the nameplate info conductors can be #6 with 60A circuit breaker?
MCA = minimum current ampacity
OCPD = maximum over current protection device

Where in the NEC doesnt reference sizing ckts per nameplate?

thanks in advance


2017 / 2014 NEC & Related Books and Study Guides

#205569 - 03/09/12 05:43 PM Re: mca and mocp nameplate [Re: Bravo]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,261
Fullerton, CA USA
NEC Article 440 is the one you want to read for this.

You can use #8 for a MCA of 46.1, with up to an 80 amp hacr breaker or fuses for the MOPD.


#205570 - 03/09/12 05:49 PM Re: mca and mocp nameplate [Re: electure]  
Bravo  Offline
Member
Joined: May 2010
Posts: 30
NY, USA
#8 is good for 40A in the 60deg C column of table 310.16. I think I need to use this for equipment rated 100A or less?


#205571 - 03/09/12 11:53 PM Re: mca and mocp nameplate [Re: Bravo]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Make sure the terminals in the Chiller are rated for 75 C if you plan on using #8 copper wire. Most equipment of this nature are only rated for 60 C and that would call for a #6. As for the line side of the disconnect (assume it is separate from the Chiller) it probably would be rated 75 and #8 would be fine. The 80a. overcurrent device is proper in either case.


George Little


Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.002s) Memory: 0.7612 MB (Peak: 0.8953 MB) Zlib enabled. Server Time: 2017-09-20 11:07:15 UTC