#205541 - 03/02/12 05:12 PM 480 v hps lighting circuit  
Cinner  Offline
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
I was working on a 480v hps lighting circuit and went to turn the circuit off to change the fixture but still measured 66 volts to ground on each leg. Does. Any one know why this would be?


Work Gear for Electricians and the Trades

#205542 - 03/02/12 06:15 PM Re: 480 v hps lighting circuit [Re: Cinner]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
What type of meter did you measure the voltage with? If it is an electronic meter with the high input impeadence, it will measure "ghost" voltages. These "ghost" voltages are due to the wires traveling next to energized wires. Both set of wires are acting as a transformer.

Measure the voltage with a Wiggy or equivalent and the voltage will PROBABLY disappear. If they do not disappear, you have a problem. If the voltage does disappear then you are measuring ghost voltages.


#205543 - 03/02/12 06:22 PM Re: 480 v hps lighting circuit [Re: Cinner]  
Cinner  Offline
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
Measured it with a fluke multimeter.


#205545 - 03/02/12 09:37 PM Re: 480 v hps lighting circuit [Re: Cinner]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Fluke multimeters ARE high impedance testers.

You need to use an old-style analog meter to load down these induced voltages. Since there is no current flow, it's really a capacitive effect.



Tesla

#205547 - 03/02/12 11:21 PM Re: 480 v hps lighting circuit [Re: Cinner]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,809
Brick, NJ USA
Cinner:

You need a 'Wiggy', or any other brand solenoid type tester, or an analog multi-meter.


John

#205550 - 03/03/12 04:26 AM Re: 480 v hps lighting circuit [Re: HotLine1]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,317
Alaska
WIGGGGGGGY!!! I carry one in my pouch just for that


"Live Awesome!" - Kevin Carosa

#205556 - 03/03/12 06:36 PM Re: 480 v hps lighting circuit [Re: Cinner]  
Lostazhell  Offline
Member
Joined: Feb 2004
Posts: 1,429
Bakersfield, CA (Originally Or...
This happens in a cogen I work in alot.. 480V wiring from VFD loads seem to induce voltage on other conductors more than anything.. HID loaded circuits have the same tendency



Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,878
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 15 (0.003s) Memory: 0.7841 MB (Peak: 0.9424 MB) Zlib enabled. Server Time: 2017-04-27 22:46:35 UTC