ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 3
Recent Posts
Feed to spa panel
by HotLine1. 06/25/17 05:28 PM
Weatherhead, POA, height?
by HotLine1. 06/24/17 02:37 PM
Windows 7 update problem
by ampherder. 06/21/17 07:01 AM
Norwegian power?
by dsk. 06/19/17 03:40 PM
Anyone ever take a Furnas A14D drum sw apart?
by gfretwell. 06/17/17 08:14 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
238,249 Are you busy
173,469 Re: Forum
166,266 Need opinion
Who's Online Now
0 registered members (), 55 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#204563 - 12/22/11 06:23 PM 1999 NEC Handbook question/Handbook search  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,326
Alaska
In the '99 cycle, Article 695: Fire Pumps, a voltage drop requirement was added to 695.7. Luck would have it that I have a '96 and '02 Handbook but not '99. If anyone of you have a '99 Handbook, can you look that up to see if they commented on this and why? I presume to protect the conductors from flaming out in the event of a lock rotor state.

Speaking of Handbooks. I am very intersted in located older NEC Handbooks and code books. I am not sure when the NFPA started to publish the Handbooks, I prefer the ones published by them.

The NFPA/NEC Handbooks I am currently looking for are:
1999
1990
1984
1978 and older

If I can not locate the Handbooks, I would probably settle for just the codebooks although I do have the 1990 and 1999.

If you have any you are willing to let go of, lets talk


"Live Awesome!" - Kevin Carosa

2017 / 2014 NEC & Related Books and Study Guides

#204564 - 12/22/11 07:57 PM Re: 1999 NEC Handbook question/Handbook search [Re: sparkyinak]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,326
Alaska
I was able to answer my own question with a little research and it is not due to the wires as my initial thought was. Does anyone want to take a stab at it?


"Live Awesome!" - Kevin Carosa

#204565 - 12/22/11 09:17 PM Re: 1999 NEC Handbook question/Handbook search [Re: sparkyinak]  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
I suspect it is because the fire pump rules allow overcurrent protection to handle LRA but if you have too much voltage drop you still might not get enough power to the pump to grind up that carp it sucked up and send it on down the line.
wink


Greg Fretwell

#204566 - 12/22/11 09:34 PM Re: 1999 NEC Handbook question/Handbook search [Re: gfretwell]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,326
Alaska
Good guess but nope. I'd probably would have never thunked it if I did not see it.


"Live Awesome!" - Kevin Carosa

#204618 - 12/25/11 01:20 AM Re: 1999 NEC Handbook question/Handbook search [Re: sparkyinak]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Under 650-7 of the 1999 handbook it reads" Voltage Drop" The voltage at the controller line terminals shall not drop more than 15 percent below normal (controller-rated voltage)under motor starting conditions. The voltage at the motor terminals shall not drop more than 5 percent below the voltage rating of the motor when the motor is operating at 115 percent of the full-load current rating of the motor.


Exception: This limitation shall not apply for emergency run mechanical starting.


There is no "Blue" highlighted wording in the handbook after this section.


#204664 - 12/28/11 04:43 PM Re: 1999 NEC Handbook question/Handbook search [Re: sparkyinak]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,833
Brick, NJ USA
I believe the "x" superscript at the upper left of 695.7 indicates that it's a change. I have to see if I still have the '99 Changes in my collections.



John

#204665 - 12/28/11 07:24 PM Re: 1999 NEC Handbook question/Handbook search [Re: sparkyinak]  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
I have the ROP and it has several pages of stuff. It looks like they rewrote the whole article. I was really looking for the substantiation of the Voltage Drop thing but no joy so far. I didn't really read the whole thing.


Greg Fretwell

#204667 - 12/28/11 08:03 PM Re: 1999 NEC Handbook question/Handbook search [Re: sparkyinak]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
John,

I still have all my old code books back to when I first started in 1981, plus someone gave me a bunch of old code books from the '56 and '47 and '75. Still have a lot of my handbooks too.

I have to check if I have the '99 changes. I am off work this week and some of this stuff is in my office.


#204668 - 12/28/11 09:31 PM Re: 1999 NEC Handbook question/Handbook search [Re: sparkyinak]  
luckyshadow  Offline
Member
Joined: Jan 2005
Posts: 305
Maryland USA
In the 1999 NEC Handbook Article 695.7 Voltage Drop, there is no commentary following it.


#204690 - 12/30/11 02:57 AM Re: 1999 NEC Handbook question/Handbook search [Re: sparkyinak]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,326
Alaska
Greg was on the right track. The changes to Article 695 was to put it in line with NFPA 20: Standard for the Installation of Stationary Pumps for Fire Protection. If you would dig into the1999 NFPA 20 and it's ROP, you would find the voltage drop requirement is to prefer the pump relay from dropping out and causing "relay chatter". That would be rather narwlly sounding on a big pump not to mentioned the lost of the pump in an emergency


"Live Awesome!" - Kevin Carosa

Page 1 of 2 1 2

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 16 (0.003s) Memory: 0.8190 MB (Peak: 0.9994 MB) Zlib enabled. Server Time: 2017-06-27 03:41:47 UTC