ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
VFD MotorFeeders
by gfretwell. 10/19/17 01:02 AM
Generator Cable Sizing
by brsele. 10/18/17 07:39 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,443 Are you busy
177,420 Re: Forum
169,010 Need opinion
Who's Online Now
0 registered members (), 10 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 3 1 2 3
#204379 - 12/05/11 11:15 PM breaker meltdown  
mikes733  Offline
New Member
Joined: Feb 2008
Posts: 3
kentucky
I had a customer call with a breaker melted to the bussbar. this was the second or third breaker that has done this according to him.the bussbar was fine but the breaker fell apart I installed a new breaker and it made good tight connection and the amp load was in range. any Ideas? I think it was a g&s panel with challenger breakers.


Work Gear for Electricians and the Trades

#204380 - 12/06/11 12:08 AM Re: breaker meltdown [Re: mikes733]  
twh  Offline
Member
Joined: Mar 2004
Posts: 919
Regina, Sask.
Load up the circuits and check the voltage drop from the feed conductor to the load conductor terminations. You'll be looking for voltages around 100 ma on the low end to about a volt, depending on the load and the size of breaker. Compare readings for the various breakers for an idea about what is normal in that panel. If the voltage drop seems high, move the probe from the feed wire to the bussbar by the breaker, then the metal part of the breaker.

It's the equivalent of checking the temperature of the connection points, but it's faster and easier to pinpoint the problem because voltage drop doesn't migrate the way heat does.


#204381 - 12/06/11 12:17 AM Re: breaker meltdown [Re: mikes733]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
Do you have a non contact thermometer? They are getting cheap enough for the mortal man and will let you further track down this heat thing. TWH is right about starting with your meter to see where the leak is.


Greg Fretwell

#204382 - 12/06/11 12:50 AM Re: breaker meltdown [Re: mikes733]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Check for corrosion on the Aluminum bus...



Tesla

#204384 - 12/06/11 09:57 AM Re: breaker meltdown [Re: mikes733]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Repeat problem and the buss doesn't seem damaged? That doesn't make sense.

However ...

1) Water dripping, condensing on the breaker might;

2) Some load that was not available to you (like a space heater) might; and,

3) the customer's own actions (not shared with you) might.


#204385 - 12/06/11 11:05 AM Re: breaker meltdown [Re: mikes733]  
mikes733  Offline
New Member
Joined: Feb 2008
Posts: 3
kentucky
thanks for the input. The bussbar was damaged from a previous breaker but the breaker I removed did not appear to have damaged the buss.I did sand the buss and applied corrosion inhibiter with the new breaker. The breaker is feeding 15 kw heat strips and is pulling 60 amps on each leg.

Last edited by mikes733; 12/06/11 11:13 AM.

#204386 - 12/06/11 11:33 AM Re: breaker meltdown [Re: mikes733]  
ghost307  Offline
Member
Joined: May 2005
Posts: 916
Chicago Illinois USA
15kW strip heaters drawing 60 Amps per phase??
What voltage are you running at?


Ghost307

#204387 - 12/06/11 12:27 PM Re: breaker meltdown [Re: mikes733]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
If you can't re-locate that breaker to an undamaged part of the buss - perhaps swapping places with a much smaller one - then you really need to replace the busses.


#204388 - 12/06/11 12:55 PM Re: breaker meltdown [Re: mikes733]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Is this a bolt-in or push in CB? 'sanding' the buss may not have been a good move. The contact tension on the push in type CB may be compromised, resulting in failure over a period of time.

If you are running 208 volt, 3 phase, with a 60 amp CB and 15KW of heat you also have an issue with the 'continuous load' (80%).

Conductor size?

Like Greg said, see if you can get your hands on an IR unit, you may have a heating issue due to the design.



John

#204394 - 12/06/11 06:55 PM Re: breaker meltdown [Re: mikes733]  
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
Since your load is linear my idea that it may be related to non linear loads is not going to explain it.
A 3 phase 15 KW load on a 60 amp breaker should be around 42 amps so the breaker looks correct for 3 phase, Single phase would be a 90 amp breaker and a 72 amp load, Note that the 90 amp breaker is actually 1/8th of an amp too much load for the 90 amp breaker but most inspectors would give that much away.



Page 1 of 3 1 2 3

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.024s Queries: 16 (0.004s) Memory: 0.8203 MB (Peak: 1.0022 MB) Zlib enabled. Server Time: 2017-10-22 10:05:29 UTC