#204183 - 11/18/11 12:56 PM strange motor current spiking problem  
Jeffdc  Offline
New Member
Joined: Nov 2011
Posts: 3
Ohio, USA
I am trying to help a customer out with this problem. There is an AC drive running a motor on a paper mill. Not 100% of the time, but frequently, during either the accel or decel, at a specific speed, the current will spike up and trip the drive. There is a 20s accel and decel time. When speed hits around 55% rated motor speed, the current will start climbing until get overcurrent fault on drive. Or, may not do this on accel, but then stop drive, and when speed drops to around 55%, get current spike and bus voltage spike, and get fault also. Can a bad motor do this?


Tools for Electricians:

#204185 - 11/18/11 06:49 PM Re: strange motor current spiking problem [Re: Jeffdc]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Is this a new install or something that just started with an existing install?
Iím no expert on the subject, but I read something somewhere about a similar issue when using deceleration in place of actual dynamic braking on a VFD motor drive with a no load condition will cause the DC bus current climb and cause a fault due to the motor acting similar to a generator.
I believe the solution was to install a dynamic brake package or simply let the motor stop on its own under no load without using deceleration function.

Maybe someone else with more first hand experience will have some info to add.


#204194 - 11/19/11 05:22 AM Re: strange motor current spiking problem [Re: Jeffdc]  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,211
SI,New Zealand
Jeff,
Is this motor part of a direct drive system or a belt drive system?
What exactly does this motor drive?
Also what brand/model/size is the motor and it's attached drive?
55% of full load speed sounds far too low on startup, and makes me wonder if the VSD has been commissioned properly.
My bread and butter is working with VSD's on motors, there isn't a problem I haven't been able to cure. wink


Let's face it, these days if you're not young, you're old - Red Green grin

#204217 - 11/21/11 11:14 AM Re: strange motor current spiking problem [Re: Trumpy]  
Jeffdc  Offline
New Member
Joined: Nov 2011
Posts: 3
Ohio, USA
Not sure brand, but motor is 150HP, goes into a gearbox (not sure ratio), then turns a shaft. There are 4 levels of rolls in this paper mill that can be engaged/disengaged with the main shaft with clutches and gears. No belts. The drive is SSD AC890.
We have ran the system with 1 level of rolls, 2 levels of rolls, etc, and seen the problem off and on with all our tests. Drive does not trip unless running with all 4 levels since overall current is lower with less than 4 levels engaged with main drive shaft.
What do you mean by 55% sounds low? The 55% is a speed when this problem seems to occur at. Other than that I am not sure what meaning it would have.
Thanks for your interest in my problem and I look forward to further discussions on this.


#204288 - 11/26/11 01:45 PM Re: strange motor current spiking problem [Re: Jeffdc]  
pdh  Offline
Member
Joined: Jan 2005
Posts: 354
Could it just be a soft start running on L-N until at sufficient speed it switches over to L-L for the remaining accel, and perhaps doing it at the wrong time?



#204291 - 11/26/11 07:37 PM Re: strange motor current spiking problem [Re: Jeffdc]  
twh  Offline
Member
Joined: Mar 2004
Posts: 905
Regina, Sask.
It might be internal to the VFD. Because the problem happens on accel and decel, it probably isn't the load driving the motor. Is the current increase actually through the motor or just line side? Do you have a line side choke installed?


#204312 - 11/28/11 01:09 PM Re: strange motor current spiking problem [Re: twh]  
Jeffdc  Offline
New Member
Joined: Nov 2011
Posts: 3
Ohio, USA
The drive output current (motor current) is what increases. Not sure if there is a choke on line side.

To give an update on this, I had the customer change the dynamic braking params because they were never setup. They said this seemed to prevent the drive from tripping but still get the current increase. They said they think there may be a mechanical problem that only shows itself at certain speeds. If I find out that it is a mechanical problem I will post that here so topic can be closed.


#204363 - 12/03/11 04:06 AM Re: strange motor current spiking problem [Re: Jeffdc]  
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 782
Chicago, Il.
http://www.pump-zone.com/motors/motors/motor-and-drive-system-resonance-problems-and-solutions.html

I am by no means an expert on VFDs but I have heard of problems with resonance. Sure sounds like that could be your problem.
Joe