ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 255 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Joined: Dec 2001
Posts: 444
S
Sandro Offline OP
Member
In interesting subject came up today.

If a fellow has a 3 phase panel, and wants to use it in his house. Could he?

The idea was to take the one phase and pick up 2 lugs, and leave the remaining phase for the third lug.

I suggested to go with single phase panel, but Im wondering if this method would be ok as well?


.

Joined: Jul 2007
Posts: 1,335
S
Member
I've seen it done several times but I wouldn't recommend it it


"Live Awesome!" - Kevin Carosa
Joined: Jul 2007
Posts: 265
W
Member
I have a 3 phase panel in my shop, using it on single phase power. Just one I had lying around when I built the shop. I only have about 5 circuits in it, so I just hooked up the a and c phases. It looks like a 3 phase high leg panel, with a blank plate in every third space. That being said I would not put a 3 phase panel in a house, just not enough breaker spaces, or if you pick up 2 phases on on leg you could be way unbalanced, not really a good idea.


Jimmy

Life is tough, Life is tougher when you are stupid
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Code wise...110.3 (B) on the red tag. That's IF there was a permit!

Along the same track, I came upon a single phase panel, om a three phase feeder and three phase loads. The genius used the isolated neutral bar for the 'c' leg!!!


John
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
It's tempting ... but technicall a no-no.

The panle lable lists the distribution systems that the panel is listed for - and yours won't make any reference to any single-phase system. Thus, the 'listing and labeling' violation.

Plus, of course, there's the usual doubled wires under one lug.

"But we'll be careful!" folks always say. I guess that most of the time they are. Good heavens, though ... panels are not that expensive!

Joined: Jun 2004
Posts: 1,273
T
Member
It's a loser...

Get the right stuff.


Tesla
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
I agree with the other Members - do not use the 3 Phase Panelboard on a Single Phase 3 Wire System.
Beside the Listing Issues & Code Issues, it is really sloppy; especially where Multiwire Circuitry &/or 2 Pole L-L Circuitry is used.

Going the opposite way - using a Single Phase 3 Wire Panelboard on a Three Phase System, has a few possible applications, which include:

Example 1:
120/240V 1 Phase 3 Wire Panelboard on 240/120V 3 Phase 4 Wire Delta System; connecting Lines A & C + Common Neutral to 1 Ph. Panelboard.
This has been done where 1 Phase loads are needed only.
No Wild Phase (Hi Voltage to Ground Phase) issues in the Panelboard.

Example 2:
120/240V 1 Phase 3 Wire Panelboard(s) on 208Y/120V 3 Phase 4 Wire Wye System; connect (2) Ungrounded Feeders + Star Point (Neutral) to Panelboard.
This is somewhat sloppy (IMO) for Commercial / Industrial stuff, however is very common in Multi-Family Dwellings, per a "Network" Service design.

Example 3:
120/240V 1 Phase 3 Wire Panelboard(s) on 240V Corner Grounded Delta System; connect the (2) Ungrounded Conductors - Phases / Lines A & C to the Bus Kit, then connect the Grounded Conductor - Phase / Line "B", to the Isolated Neutral kit.
Line "B" is used as a Common, where (2) 1 Phase 2 Wire loads are connected, as described in the following Illustration:

[Linked Image]

Refer to Corner Grounded 3 Phase 3 Wire Delta, at the Tech. reference section for more information.

Forgot to add...

The latter example (Example #3) would require 1 Pole devices with a Single Pole AIC rating at no less than 240V.

Furthermore, the Panelboard must be Listed for such use.

Also, this setup _SHOULD NOT_ be used where the Neutral Kit is connected to an Ungrounded Conductor.

This setup was common "Back In The Old Days" (installed up to circa 1980), and may still be found existing in "Older" Industrial areas.


-- Scott

Last edited by Scott35; 10/05/11 12:44 AM. Reason: Included the added notes

Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Great description Scott, as usual.

I haven't had any experience with that apartment house system but I have heard a lot about it. Usually people wondering why their heating appliances don't work right. wink

The others I have seen a lot of. The corner delta is common on those pumping stations you see along the road (all 3p L/L load). We also have a lot of red leg here, in light industrial bay areas and they usually have a 3p panel in the shops and a 1p panel for the house loads and offices.


Greg Fretwell
Joined: Jul 2007
Posts: 1,335
S
Member
I have also come across 3 phase panels on ungrounded single phase systems where the center bus was the neutral and since it was not grounded, it had to have OCPD's and yes the breakers were rated for switching the neutral


"Live Awesome!" - Kevin Carosa
Joined: Feb 2002
Posts: 2,233
H
Member
I have seen one installed in a firehouse with 2 lugs on 1 phase. That made 30 breakers on 1 leg and 15 on the other. The panel was very unbalanced. That panel is still in operation today, I believe. Not a good installation, I doubt it was ever inspected.