ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 3
dsk 3
Recent Posts
Feed to spa panel
by HotLine1. 06/25/17 05:28 PM
Weatherhead, POA, height?
by HotLine1. 06/24/17 02:37 PM
Windows 7 update problem
by ampherder. 06/21/17 07:01 AM
Norwegian power?
by dsk. 06/19/17 03:40 PM
Anyone ever take a Furnas A14D drum sw apart?
by gfretwell. 06/17/17 08:14 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
238,235 Are you busy
173,449 Re: Forum
166,256 Need opinion
Who's Online Now
0 registered members (), 62 guests, and 14 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#200697 - 04/14/11 11:54 PM Service Disconnect  
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
A Service Main disconnect could be outside the building or in the Bldg. right?
If the main is outside (near a transformer)then the first panel it feeds in the Bldg. would be a sub panel?
SJT


2017 / 2014 NEC & Related Books and Study Guides

#200700 - 04/15/11 02:09 AM Re: Service Disconnect [Re: SJT]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
Technically the service disconnect just has to be on the property but your AHJ may still want a disconnect on/in the building.
Yes that will become a feeder and you need to run the ECG along with a ground. As long as that is the feeder for the whole building, you can use 210.15(B)(6) in a dwelling. (Not commercial)

Last edited by gfretwell; 04/15/11 04:04 AM. Reason: Make the correction Niko pointed out

Greg Fretwell

#200701 - 04/15/11 03:36 AM Re: Service Disconnect [Re: SJT]  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Greg meant, 310.15(B)(6) for 2008 and 310.15(B)(7) for 2011


Be kind to your neighbor, he knows where you live


#200703 - 04/15/11 04:06 AM Re: Service Disconnect [Re: SJT]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
Thanks. I guess I should turn up the light when I type

I am not on the 2011, in protest of the CD thing wink


Greg Fretwell

#200714 - 04/16/11 12:00 AM Re: Service Disconnect [Re: SJT]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,833
Brick, NJ USA
Be cautious on the location 'within the building'. Unprotected, unfused, conductors within a building, the distance allowed is not specific in the NEC. For the most part, it's left up to the local AHJ. I hear 12", 5', 3'4", but there is NO distance within the book & never was.

A main inside is accepted 'nearest to the point of entry', unless we use the 2" of concrete/brick exception. It all boils down to the AHJ's 'nearest' definition


John


Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.7691 MB (Peak: 0.9093 MB) Zlib enabled. Server Time: 2017-06-26 17:22:35 UTC