480 V Branch circuit and 120V branch circuit #200601
04/09/11 07:46 PM
04/09/11 07:46 PM
L
lite bulb  Offline OP
Member
Joined: Feb 2006
Posts: 78
wilm,de.
Can 480V and 120V branch circuits share the same raceway. The 480V branch circuit is being fed from the MCC panel operates four .50 amp vibrators and the 120V is being fed from the lighting panel for a flood light, both go to a common jbox within the same room then from there they go underground outside the building to the vibrators and flood light.

2017 / 2014 NEC & Related Books and Study Guides
Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb] #200605
04/09/11 10:42 PM
04/09/11 10:42 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
And the answer is: Yes, and the code reference is Article 300 Section 300.3(C)(1). 2008 NEC


George Little
Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb] #200626
04/10/11 08:20 PM
04/10/11 08:20 PM
L
lite bulb  Offline OP
Member
Joined: Feb 2006
Posts: 78
wilm,de.
Thanks George for the reply.

Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb] #200638
04/11/11 08:23 AM
04/11/11 08:23 AM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Yeah,

Now how about a 120/240 volt and a 12 volt circuit?

Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb] #200642
04/11/11 07:12 PM
04/11/11 07:12 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
Sure as long as you don't want it to be class 2 or 3.


Greg Fretwell
Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb] #200644
04/11/11 07:31 PM
04/11/11 07:31 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
You beat me to it Greg. As for the substantiation it would be 725.48.


George Little
Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb] #200662
04/13/11 09:19 AM
04/13/11 09:19 AM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,

Now would you please tell that to some of the EC's in my area. They put 16 ga bell wire in with 120 volt wiring and think that it is OK. I also inspect premade shelters for cell towers and in there they have the low voltage bell wire mixed in with the service conductors. I guess the are using the sec. 725.48.

Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb] #200666
04/13/11 12:15 PM
04/13/11 12:15 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
How are they putting them together? You could make the argument that if both are cables you have separation but they still have to terminate in separate compartments.

Using the class 1 rules basically means you are using low voltage on a chapter III wiring method.
"Bell wire" can't be used in Class 1.


Greg Fretwell
Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb] #200678
04/13/11 10:59 PM
04/13/11 10:59 PM
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
if two different systems enter a jbox, they still have to have a divider?

Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb] #200719
04/16/11 01:32 PM
04/16/11 01:32 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,

The cell tower pre-made control box had bell wire in the same cabinet with service cable and there were no separate boxes, areas or compartments. Next time I inspect a cell tower trailer, I will see if I can get a picture.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,587 Are you busy
180,382 Re: Forum
170,859 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 16 (0.004s) Memory: 1.0226 MB (Peak: 1.2039 MB) Zlib enabled. Server Time: 2018-01-22 02:26:23 UTC