#200601 - 04/09/11 08:46 PM 480 V Branch circuit and 120V branch circuit  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
Can 480V and 120V branch circuits share the same raceway. The 480V branch circuit is being fed from the MCC panel operates four .50 amp vibrators and the 120V is being fed from the lighting panel for a flood light, both go to a common jbox within the same room then from there they go underground outside the building to the vibrators and flood light.


2017 / 2014 NEC & Related Books and Study Guides

#200605 - 04/09/11 11:42 PM Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
And the answer is: Yes, and the code reference is Article 300 Section 300.3(C)(1). 2008 NEC


George Little

#200626 - 04/10/11 09:20 PM Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb]  
lite bulb  Offline
Member
Joined: Feb 2006
Posts: 78
wilm,de.
Thanks George for the reply.


#200638 - 04/11/11 09:23 AM Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Yeah,

Now how about a 120/240 volt and a 12 volt circuit?


#200642 - 04/11/11 08:12 PM Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,103
Estero,Fl,usa
Sure as long as you don't want it to be class 2 or 3.


Greg Fretwell

#200644 - 04/11/11 08:31 PM Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
You beat me to it Greg. As for the substantiation it would be 725.48.


George Little

#200662 - 04/13/11 10:19 AM Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,

Now would you please tell that to some of the EC's in my area. They put 16 ga bell wire in with 120 volt wiring and think that it is OK. I also inspect premade shelters for cell towers and in there they have the low voltage bell wire mixed in with the service conductors. I guess the are using the sec. 725.48.


#200666 - 04/13/11 01:15 PM Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,103
Estero,Fl,usa
How are they putting them together? You could make the argument that if both are cables you have separation but they still have to terminate in separate compartments.

Using the class 1 rules basically means you are using low voltage on a chapter III wiring method.
"Bell wire" can't be used in Class 1.


Greg Fretwell

#200678 - 04/13/11 11:59 PM Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb]  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 216
Washington...Not DC
if two different systems enter a jbox, they still have to have a divider?


#200719 - 04/16/11 02:32 PM Re: 480 V Branch circuit and 120V branch circuit [Re: lite bulb]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,

The cell tower pre-made control box had bell wire in the same cabinet with service cable and there were no separate boxes, areas or compartments. Next time I inspect a cell tower trailer, I will see if I can get a picture.


Page 1 of 2 1 2

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 16 (0.003s) Memory: 0.8171 MB (Peak: 0.9990 MB) Zlib enabled. Server Time: 2017-08-20 07:43:33 UTC