#200459 - 04/02/11 01:56 AM Dropping 1 leg of 480 to control site lighting  
wewire2  Offline
Member
Joined: Nov 2002
Posts: 244
California
Is there a code reference that prohibits dropping 1 leg of a 480 circuit to control HID lighting? I notice 410.141(B) only applies to fixtures exceeding 1000V.


2017 / 2014 NEC & Related Books and Study Guides

#200480 - 04/02/11 10:37 PM Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,809
Brick, NJ USA
Wewire2:

Care to explain the above with a little more clarity please.


John

#200485 - 04/02/11 11:39 PM Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2]  
wewire2  Offline
Member
Joined: Nov 2002
Posts: 244
California
Sure, thanks John.
3 phase 480, 3 wire is pulled to a light pole with 4
fixtures on the pole. The site engineer wants to drop legs to control the lights separately. I don't like the design but can't seem to find anything that prohibits it as long as the required disconnecting means is in place. What do you think?


#200486 - 04/03/11 01:05 AM Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Look at 410.104(B). I don't know if it applies but it could. Not sure what the Design Professional has in mind but this might help.

Last edited by George Little; 04/03/11 01:06 AM.

George Little

#200488 - 04/03/11 02:10 AM Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2]  
wewire2  Offline
Member
Joined: Nov 2002
Posts: 244
California
George, I think that's what I'm looking for. The "auxiliary
equipment" terminology threw me off and I skimmed right past it. It appears that the term auxiliary equipment refers to ballast. Thank you sir!

410.104(B)Where supplied by ungrounded conductors of a circuit, the switching device of auxiliary equipment shall simultaneously disconnect all conductors.



Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.7680 MB (Peak: 0.9111 MB) Zlib enabled. Server Time: 2017-04-25 14:40:25 UTC