Dropping 1 leg of 480 to control site lighting #200459
04/02/11 12:56 AM
04/02/11 12:56 AM
W
wewire2  Offline OP
Member
Joined: Nov 2002
Posts: 244
California
Is there a code reference that prohibits dropping 1 leg of a 480 circuit to control HID lighting? I notice 410.141(B) only applies to fixtures exceeding 1000V.

2017 / 2014 NEC & Related Books and Study Guides
Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2] #200480
04/02/11 09:37 PM
04/02/11 09:37 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,917
Brick, NJ USA
Wewire2:

Care to explain the above with a little more clarity please.


John
Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2] #200485
04/02/11 10:39 PM
04/02/11 10:39 PM
W
wewire2  Offline OP
Member
Joined: Nov 2002
Posts: 244
California
Sure, thanks John.
3 phase 480, 3 wire is pulled to a light pole with 4
fixtures on the pole. The site engineer wants to drop legs to control the lights separately. I don't like the design but can't seem to find anything that prohibits it as long as the required disconnecting means is in place. What do you think?

Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2] #200486
04/03/11 12:05 AM
04/03/11 12:05 AM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Look at 410.104(B). I don't know if it applies but it could. Not sure what the Design Professional has in mind but this might help.

Last edited by George Little; 04/03/11 12:06 AM.

George Little
Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2] #200488
04/03/11 01:10 AM
04/03/11 01:10 AM
W
wewire2  Offline OP
Member
Joined: Nov 2002
Posts: 244
California
George, I think that's what I'm looking for. The "auxiliary
equipment" terminology threw me off and I skimmed right past it. It appears that the term auxiliary equipment refers to ballast. Thank you sir!

410.104(B)Where supplied by ungrounded conductors of a circuit, the switching device of auxiliary equipment shall simultaneously disconnect all conductors.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
sparky 22
Admin 20
Potseal 13
Popular Topics(Views)
243,530 Are you busy
180,332 Re: Forum
170,823 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.9663 MB (Peak: 1.1081 MB) Zlib enabled. Server Time: 2018-01-18 04:04:51 UTC